Coleman No Defrost - HVAC - DIY Chatroom Home Improvement Forum
Old 02-06-2013, 07:02 PM   #1
Coleman no defrost
Ok new coleman 5 ton heat pump with defrost problems, has the new demand defrost board where the ambient sensor and the coil sensor work together to figure out if the machine needs to defrost, board number 1157-83-9021a , i already changed the board and i always change the defrost sensor but i did not change the ambient sensor , so as right of now no defrost i understand that the pin sitting is suppose to be on 1 but what does the letter p do
uncletink is offline   Reply With Quote
Old 02-06-2013, 07:27 PM   #2
An old Tradesmen
Rewards Points: 6,072
P is programmed. Thats what is used when the board is installed at the factory. it means it was programmed specifically for that unit.
So are you saying it neers goes into defrost. not even its 6 hour compressor run time defrost? Or that the coil seems to frost up a lot, and you don't see it defrost.
Old 02-06-2013, 07:33 PM   #3
AKA HVACTECHFW
Rewards Points: 1,208
will the unit defrost if you short the test pins?
It does not matter what the other pins do where the jumper is. York/coleman says that it should be on 1 so that is what it needs to be on.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 02-06-2013, 08:06 PM   #4
no defrost cycle at all put the board on over 12 hrs ago, even through the test pin nothing, the curve is set at 1 just like york said , im just wondering if i change the ambient sensor if it would work
Old 02-06-2013, 08:29 PM   #5
An old Tradesmen
Might. The board needs to see X degree difference between ambient and liquid line temp, or it won't go into defrost. Except for its 6 hour of compressor run time. Which it won't do, it the ambient sensor indicates its above X degrees outside.
Help My Admiral Refrigerator is leaking water Cuwillis Appliances 10 03-25-2014 09:21 AM
Tempstar heat pump won't initiate defrost cycle lgmccoy1 HVAC 14 12-08-2011 07:07 PM
Using Gas heat during Defrost mgroves HVAC 15 12-18-2010 06:51 PM
Need help from control guys or heat pump gurus (reversing heat pump defrost cycle) pomelo HVAC 11 03-08-2010 09:13 PM
Kenmore fridge not cooling, freezer ok bobvanhalder HVAC 7 10-22-2008 11:52 PM