Old 12-31-2011, 04:21 PM   #16
I'm Your Huckleberry
Rewards Points: 2,270
It could be, yes.
Turn the breaker to the furnace off. Remove the face plate of the stat, exposing the low voltage wires and the terminals they're connected to. You can use a gator clips and jump the R terminal to the W terminals or uses a thin wire and simply screw it to each terminal. This should bring on the heat.
Turn the breaker back on. Until you remove that jumper the system should run in heating mode. See if that works.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 12-31-2011, 04:24 PM   #17
Originally Posted by Tator1076 View Post
You may have stat problem but some of those units if it went out on lock out and once you cut the unit off by tstat or switch it will reset board. Also that may have a smart valve gas valve on it.
I already checked, no smart valve.
Scroll down.
http://mobilehomefurnace.com/zcart/i...ducts_id=14586
Thanks.
Old 12-31-2011, 04:31 PM   #18
HVAC Tech/ Browns Fan
I hate smart valves . I just change 3 of them in the past 2 weeks on Armstrong.
Tator1076 is offline   Reply With Quote
Old 12-31-2011, 04:35 PM   #19
I have one on the truck I picked up yesterday for a Consolidated. Going in tomorrow or Monday.
Thanks.
Old 12-31-2011, 07:30 PM   #20
Disconnected all the t-stat wires from the board. Cycled the power switch. Still got the rapid blinking LED. I suppose it could be a bad board. But why does it keep blowing the board?
IUFAN87 is offline   Reply With Quote
Old 12-31-2011, 08:28 PM   #21
with the stat in the off position, jump the r and the W on the board for heating sequnce to begin. R to G for fan on only and R to Y for coOling.
See if you can control any function at aLl at the board, blinking light or not.
When you changed the board you may not have grounded yourself proior to handling it. You need to discharge any static electricity from your body before handling any circuit board and even than only handle the board by the edges.
Thanks.
Old 12-31-2011, 08:46 PM   #22
Ok, t-stat off. Jump r to w, relay clicks for the blend air motor and thats it. r to g nothing happens. R to Y the compressor on the a/c unit outside kicks on but thats it.
LED is rapid flashing the whole time btw.
Old 12-31-2011, 08:58 PM   #23
This is the 4th or 5th board to be replaced on this furnace. Never had the rapid flashing LED until the previous board and this one. And this board didnt have any problems until a day or two after it was installed. Just wondering if there could be another componet on the furnace causing the board failure?
Old 12-31-2011, 09:05 PM   #24
Pull the tube off of the inducer motor (you called it BLEND) and suck on the hose while the system is on call for heat. You will be applying negative air pressure to the pressure switch and closing it, what the inducer motor is supposed to do, and thus allowing the rest of the heat sequence to begin.
See what happens.
Thanks.
Old 12-31-2011, 09:18 PM   #25
See what happens.
Well theres no tube small enuf to put my mouth around on it. Just an insulated duct bout 6 inches in dia. Course now the LED isnt blinking and the furnace is working as it should.......Anyone got a stick of dynamite? lol
Old 12-31-2011, 09:21 PM   #26
Something is taking out that board, like the blower motor itself. Is there a good ground (wire) to the unit and on the board?
Thanks.
Old 12-31-2011, 09:22 PM   #27
If you have an inducer, you have that hose.
Thanks.
Old 12-31-2011, 09:24 PM   #28
Thanks.
Old 12-31-2011, 09:37 PM   #29
I wonder if it's a hertz/frequency rate thing?
Thanks.
Old 12-31-2011, 09:45 PM   #30
nope nuttin like that. The one i have sits on top of the furnace. It has something to do with blending fresh air? doesnt actually look like a motor. but it can be switched to fresh air or not. It has two blue wires going to it.
Brand new Coleman 97.5% furnace makes horrible whining noise junebuggy HVAC 10 11-15-2016 09:53 AM