Coleman Furnace Problems - HVAC - DIY Chatroom Home Improvement Forum
Old 12-30-2011, 03:31 AM   #1
Coleman furnace problems
I have a coleman furnace model #DGAT090BDD. My roof leaked water onto it and damaged the high limit switch and the control module. The green LED on the module was flashing rapidly. I replaced both the module and the limit switch. The furnace worked fine for a few days. But it started doing the rapid flashing of the LED again. I can manually cycle the power off and back on and sometimes it works fine for about 24 hours. But cycling the power off and back on doesnt always help. Sometimes as soon as I cycle the power switch it starts the rapid blinking again, and the furnace wont function. What could be causing this?
IUFAN87 is offline   Reply With Quote
Old 12-30-2011, 04:21 AM   #2
An old Tradesmen
Rewards Points: 8,236
Count the flashes, they are an error code. then look at the code legend and see what it says.
Old 12-30-2011, 07:13 AM   #3
Thanks for the reply. But this is not like a typical error code. There is no discernable "blink" of the LED. It actually isnt an "on/off" blink. Its more like a constant bright/dim, and very rapid flash.Thats what I dont understand about it. It has had diagnostic codes I have repaired in the past. One was for automatic ignition failure one time. The other was for limit cycling. Which has happened several times.
Old 12-30-2011, 07:34 AM   #4
I'm Your Huckleberry
Rewards Points: 2,270
check the transformer. Pull the transformer wires off of the control board and with power to the transformer see if it's putting out a steady 24 volts. It may be fluctuating, going bad due to moisture contamination.
Don't let the wires touch any metal or you will need a new one.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 12-30-2011, 07:36 AM   #5
Actually you don't even need to pull them off (risking chance of yourself getting electricuted and yes, 24 volts stings a bit), simply check across the R and the C terminal on the board for a steady 24 volts.
Thanks.
Old 12-30-2011, 07:37 AM   #6
I'd also check the high voltage coming into the furnace. Start with the basics.
Thanks.
Old 12-30-2011, 09:02 AM   #7
Sounds to me like you have a much bigger problem......That limit is a safety device that trips when the furnace has reached a dangerous temperature. just replacing the limit is NOT how you address a tripped limit.....you must determine why the limit is tripping, then correct the issue.
harleyrider is offline   Reply With Quote
Old 12-30-2011, 09:08 AM   #8
I should have clarified on the limit switch code i was getting. My roof has leaked on different occasions over the years. The water damaged the high limit switch which set the limit cycling code. Thanks
Old 12-30-2011, 10:28 PM   #9
Just almost like clock work the green LED started the rapid flashing again this evening. Checked the voltages in and out of the transformer. Steady 27 out at the transformer and steady 120 in. As soon as I cycled the power switch off and back on the furnace kicked on and worked normal. Anymore ideas would be appreciated. thanks
Old 12-31-2011, 03:36 AM   #10
An old Tradesmen
Check you line voltage grounding.
Old 12-31-2011, 08:08 AM   #11
sleepyg's Avatar
Rewards Points: 26
If you can "power cycle" (turn off the main power) the unit and it runs some of the time and other times it does not, then I would lean toward having a bad limit or the board is bad.
When you drop the power you release all the electronics to a normal state. When you make the system "call" for heat you start a sequence and when the sequence is not completed you get your flashing light. Use the wiring digram and trace the sequence of how it should start and if it goes to the control board and stops then what on the board stopped it? Could be the limit or could be a bad relay on the board.
Was any moister left behind after you installed the new parts? A little water will do a lot of damage to printed circuit boards.
Sorry for the long reply.
sleepyg is offline   Reply With Quote
Old 12-31-2011, 09:09 AM   #12
Thank you for the reply sleepyg. It was completely dry when I installed the new board and hasnt gotten wet since. Like I said it worked fine for a few days. Sometimes I can cycle the power and it will start working. At the moment it is not working. I cycle the power switch and it continues the rapid blinking. I will do some more troubleshooting. Thanks so much for the advice.
Old 12-31-2011, 02:42 PM   #13
I'd remove the thermostat from circuit when diagnosing.
Thanks.
Old 12-31-2011, 04:10 PM   #14
Doc, are ya thinkin the t-stat cud be the problem? Because last night I woke up and it was cold in the house. I checked and the LED wasnt blinking. I checked the thermostat. It was set at 70. So I pulled it back til I heard it click. Temperature was at like 58. I then heard the furnace start working.
Old 12-31-2011, 04:17 PM   #15
HVAC Tech/ Browns Fan
You may have stat problem but some of those units if it went out on lock out and once you cut the unit off by tstat or switch it will reset board. Also that may have a smart valve gas valve on it.
Tator1076 is offline   Reply With Quote
Brand new Coleman 97.5% furnace makes horrible whining noise junebuggy HVAC 10 11-15-2016 09:53 AM
Lennox ghr26 furnace problems wayfis HVAC 8 01-05-2010 05:51 PM
coleman mobile home furnace smurfette HVAC 2 11-01-2009 08:10 PM
hiel furnace problems plumbfitter HVAC 5 08-31-2009 09:54 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 01:55 PM