Coleman Echelon 9V - High Fan Speed In Low Stage?? - HVAC - DIY Chatroom Home Improvement Forum
Old 12-02-2010, 11:46 AM   #1
Coleman Echelon 9V - high fan speed in low stage??
Have a Coleman Echelon 9V in 120,000 Btu 2 stage furnace.
Connected to a two stage thermostate properly configured.
Calls for w1 and w2 heat are correctly applied to furnace.
Only problem is that the furnace runs on the high speed when only w1 heat is called for. Adjusting the thermostat to call for w2 heat works but the blower speed is the same, i.e. on high
It is supposed to run on the low speed of approx 1400 rpm instead of the approx 2100 rpm on high.
Any suggestions??
Car Guy is offline   Reply With Quote
Old 12-02-2010, 04:38 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,818
Yes, if it is running too fast on low fire it will cool down the heat exchanger too much and damage it.
Old 12-02-2010, 06:30 PM   #3
I was under the impression that too much heat will damage the heat exchanger and not allowing it to cool down a bit after the burner cuts out.
I don't understand what mechanism would damage the heat exchanger from insufficient heating.
In any case I am waiting for a qualified service technician to complete the install wit the gas pressure, heat rise, fan speed etc adjustments.
Anyone have an idea of what room heat register temperatures should be on low and high? Realizing that distance from the furnace makes a bit of difference......what is a reasonable range of outlet temp that is workable.
Old 12-02-2010, 06:59 PM   #4
Hvac Pro
yuri's Avatar
If it runs too cool moisture in the exhaust will condense into water prematurely in the primary heat exchanger and corrode it etc. Supposed to stay warm and condense in the secondary exchanger which is stainless steel and designed for water.
Old 12-02-2010, 08:54 PM   #5
I have switched it from the max "A" profile to the "C" profile and the motor rpm change is now noticeable from low to high.
Room outlet temperatures are in the 90 degree range depending on closeness to the furnace.
The ducting above the furnace is in the 100 degree range so a temp rise of about 30 degrees and I believe the specification on the plate on the inside of the front panel door is 40 - 70 on both low and high fire.
I am probably on the low side of the range. Using an infrared temp measuring device which reads a bit low on the outside of the duct. Inside duct will be higher. Vent temps should be petty accurate.
Anyway the noise level is way down and the motor ramps up as it is supposed to on high and ramps down on low and is within a reasonable range as per the temp rise criteria.
So we shall wait for the service guy to do the final tuning.
Old 12-02-2010, 09:08 PM   #6
Hvac Pro
yuri's Avatar
Sounds good to me. I try get them in the middle of the range ie: 50-60 deg rise. Usually around 125-130 deg supply temp is normal.
Old 12-03-2010, 01:36 PM   #7
Thanks for your response yuri.
Old 12-03-2010, 02:28 PM   #8
Hvac Pro
yuri's Avatar
Your welcome. Make sure the tech uses a manometer for the gas pressure and stick thermometer in the ductwork to properly set it up and watch him. Some don't know how or just "talk the talk".
how to build a single phase induction motor sashman Electrical 3 03-31-2011 07:18 AM
Trane XV80 - low speed fan not working oregondean HVAC 4 01-12-2009 12:46 PM
Question about regular & high speed USB's mact60 PC Repairs & Upgrades 3 08-01-2008 05:55 PM
Two Speed Compressors rjordan392 HVAC 2 08-26-2007 01:32 AM
Slowing fan motor speed in air handler Manuel6 HVAC 7 04-17-2007 09:01 AM