Hi. We have a gas furnace with a code 33. The problem is that once it calls for heat it goes on for exactly 10 min, shuts of for exactly 1 min., then back on, 10 min, 1 min, continually, until it reaches temp, which can be quite long.
Technician replaced the main computer board - didn't help. Any thoughts??
mijakb is offline   Reply With Quote
Old 11-21-2011, 06:06 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 396
If it is a Carrier/Bryant/Payne code 33 is open limit. means that not enough air is moving thru the furnace and it is cycling on the limit control. dirty ac coil, filters,ducts, vents closed could be the problem.
Old 11-21-2011, 06:14 PM   #3
checked those things, but all seem to be fine. Heres one more piece that we just figured out. It only happens when the downstairs calls for heat, not upstairs. Thermostat was already replace downstairs, as we thought that was the original problem, but still continues.
Old 11-21-2011, 06:26 PM   #4
Hvac Pro
yuri's Avatar
Rewards Points: 396
I assume you have 2 furnaces? Yes?
Remove the tstat from the problem one and pack pink fibreglass insulation in the hole behind it in the wall. You may be getting a draft thru there and aggravating the tstat.
code 33 is temp related so it has to be a problem with airflow. if they share the same return air duct then one may be overpowering the other.
Old 11-21-2011, 06:57 PM   #5
Hi Yuri.
No, we have one furnace with 2 zones. Is there a door?? for zone 1 and for zone 2?
Old 11-21-2011, 07:12 PM   #6
Hvac Pro
yuri's Avatar
Rewards Points: 396
I would literally have to see your setup. In some cases they have a "barometric damper" bypass pipe from the supply plenum so the excess air that gets blocked when 1 zone/damper closes can bypass back into the return duct. if that is out of whack/sticking or not set properly that may be why it is overheating.
Old 11-21-2011, 07:17 PM   #7
Okay. Thanks Yuri. We'll have to contact someone here to help with that. I appreciate your response. I'll post the outcome.
Old 11-21-2011, 07:21 PM   #8
Hvac Pro
yuri's Avatar
Rewards Points: 396
Good Luck.
Make sure you ask them if they have worked on zoned systems as they are rare and most guys don't see them or know them well. Talk to the service manager and explain what you have.
Carrier furnace help code 13 mudtruck HVAC 10 11-23-2013 02:24 PM
Payne furnace -- Error Code 12 orcaboy HVAC 22 03-11-2011 05:18 PM
Carrier Furnace help code 31 fauxjaux HVAC 6 04-22-2010 10:36 PM
Carrier 58MCA Furnace No Heat (Error 33) zerafah49 HVAC 1 12-10-2008 07:32 PM
Error code flashing on Lennox furnace Head Scratcher HVAC 6 03-27-2008 05:24 PM