Hi,
When the blower turns on, the furnace (seems to come from the gas control valve) makes continuous clicking sounds like crazy and then the flame just goes out. See the youtube video:
http://www.youtube.com/watch?v=QJN4ZctNv7g
Need some idea. Thanks.
dragonballusa is offline   Reply With Quote
Old 09-25-2012, 04:29 AM   #2
Professional
sounds is likely from the gas valve and is most likely due to the pressure switch barely making. Check your flue and make sure it is not obstructed in any way. Does the inducer (motor above the burners) seem to be running at the correct speed? Other than that the heat exchanger will need looked at (by a pro) and the pressure at the pressure switch needs verified with a manometer (by a pro).
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 09-25-2012, 05:50 AM   #3
An old Tradesmen
Yep, have the heat exchanger checked.
Old 09-25-2012, 07:25 AM   #4
is that a red tag to the right of gas valve....it would have been placed there by gas company,,,for a dangerous condition on the furnace.....how long has this been doing this....agree with all have heat exchanger checked,,and gas valve.....
Old 09-25-2012, 08:06 AM   #5
biggles's Avatar
is that induced draft if so check the pressure switch something is bouncing the 24V to the main gas...if it is doing the same thing over and over it has to be a control....check for loose control wires something is bouncing..
Old 09-25-2012, 10:23 AM   #6
Here is another video showing at the beginning of the heat cycle, no clicking after the burner is on.
http://www.youtube.com/watch?v=h-Y-nljf0GA
The clicking starts when the blower kicks in.
If I open the cover to the lower chamber where the blower and control panel are located, the burner flame will not go out and the clicking sound is less frequently.
Old 09-25-2012, 10:52 AM   #7
Professional
Get the heat exchanger checked asap! Do not use your furnace until you do so!
IT IS WHAT IT IS
Old 09-25-2012, 11:59 AM   #8
An old Tradesmen
Post brand and model of furnace. Bu you need to have that heat exchanger checked. its probably bad.
Old 09-25-2012, 12:12 PM   #9
shut down furnace ....have heat exchanger checked......do not use it till you do.....
Old 09-25-2012, 12:17 PM   #10
Thanks all for the advice. The technician will be in today.
The Following 2 Users Say Thank You to dragonballusa For This Useful Post:
ben's plumbing (09-25-2012), hvactech126 (09-25-2012)
Old 09-25-2012, 06:03 PM   #11
Clean your flame sensor
danpik is offline   Reply With Quote
Old 09-25-2012, 06:06 PM   #12
An old Tradesmen
A dirty flame sensor would cause the burners to lock out after X tries. His isn't going back into purge mode, so its not his flame sensor.
Old 09-25-2012, 06:50 PM   #13
The technician has left. The problem is caused by a loose wire in the control panel. Once the connection is tightened, the furnace is working properly.
The Following User Says Thank You to dragonballusa For This Useful Post:
Old 09-25-2012, 08:21 PM   #14
An old Tradesmen
Good news for you. But please post brand and model number of furnace.
Old 09-25-2012, 10:47 PM   #15
Trane XE 80 Model TUD120C960J
Water Inside/Around American Standard Furnace michrob HVAC 8 12-08-2011 04:51 PM
Ruud furnace issue on upgrade board and flame sensor rubberman HVAC 22 01-16-2010 12:34 AM
Furnace Ignitor Was Clicking While Lit, Now Won't Light scribb HVAC 13 10-12-2009 02:00 AM
Miller G5RA furnace flame sensor problem mpit52 HVAC 3 01-16-2009 11:30 AM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM