Clicking Noise - Nothing Running On Outside Unit - HVAC - DIY Chatroom Home Improvement Forum
Old 08-26-2013, 09:20 AM   #1
Clicking Noise - nothing running on outside unit
When I went to turn on the AC this morning, I got fan only - nothing outside. I opened up the panel, and there is a clicking noise (coming from the part I took a picture of) when I turn it on/off and a very faint humming noise. I replaced the capacitor last year.
Any help would be appreciated.
jason586 is offline   Reply With Quote
Old 08-26-2013, 09:37 AM   #2
PoleCat's Avatar
Rewards Points: 1,646
Check for 240V across that red and black wire at the top side of your contactor.
"Ask me anything. If I don't know the answer I'll make something up."
PoleCat is offline   Reply With Quote
Old 08-26-2013, 09:53 AM   #3
Hvac Pro
yuri's Avatar
Rewards Points: 1,402
actually you want to go to the bottom side of the contactor (black and white wires) as that is incoming. if you have no 240 volts then check your fuses/breakers or disconnect or just do that anyway.
Old 08-26-2013, 07:42 PM   #4
biggles's Avatar
shut the disconnect out on the condenser...then call the cooling in from the stat this will give you 24Vs at the contactor shown..if it is chattering you won't short cycle that compressor..or fan.remove one side of the LOW voltage slip connectors and touch it on and off...looking for a once closure and having I hold with it connected....if not the coil is weak easy local Grainger trip and change out single pole 24V contactor 30amps rated for 230V
Old 08-27-2013, 01:26 PM   #5
Here is a pic of what I got across the white and black at the bottom of the contactor when the AC is NOT turned on and the center section of the contactor is NOT recessed in.
When I turn the AC on and the contactor clicks/center section recesses in, the reading goes to zero.
Old 08-27-2013, 03:40 PM   #6
voltage is wrong or i've been using a digital for so long i've forgotten how to read an analog. lol.
on your meter i assume 250v is full scale, you have about 105v. check fuses for continuity and 110v to gd from each leg.
hvac5646 is offline   Reply With Quote
The Following User Says Thank You to hvac5646 For This Useful Post:
ben's plumbing (08-27-2013)
Old 08-27-2013, 05:09 PM   #7
Hvac Pro
yuri's Avatar
Yep, you got about 80 volts when I enlarge the pic. One of your fuses is blown or one leg of the twin breaker is tripped.
The Following User Says Thank You to yuri For This Useful Post:
Old 08-27-2013, 07:15 PM   #8
The breaker is not tripped, so I guess it is one of the fuses.
How can I check the fuses. Using the voltmeter?
Old 08-27-2013, 07:29 PM   #9
Rewards Points: 50
arnt they cheap enough just to by 2 and replace? also have spares?
10 bucks on Amazon 2 pack free ship
digitalplumber is just a name for use here, I am not a plumber!
digitalplumber is offline   Reply With Quote
Old 08-27-2013, 08:04 PM   #10
An old Tradesmen
Rewards Points: 6,464
On your meter, you will see a setting that looks a bit like an upside down horse shoe. that is the ohms setting. Set it to that, and check if the fuses are open(the needle will remain to the left side.
The Following User Says Thank You to beenthere For This Useful Post:
Old 08-27-2013, 08:05 PM   #11
Hvac Pro
yuri's Avatar
1) shut off breakers inside house
2) check for voltage from each side of the fuse to ground /metal box with no paint on it to make sure it is not live
3) wear leather gloves and boots and carefully remove/pull the fuse out when ground is dry (not standing on wet grass)
4) check across the fuse with the ohmmeter function of the meter. looks like an upside down U . or google how to use an ohmmeter for some vids. should have 0 ohms or very little resistance if not blown. infinite resistance if blown. replace both of them and HDepot may have them, not 100% sure but they have some.
Old 08-27-2013, 08:06 PM   #12
I had not looked up how much they cost yet. I wanted to know how to test them just to make sure they tested bad and were the problem, plus then I would know how to do it if needed in the future.
It is supposed to 90 tomorrow with the low of 78 tomorrow evening, so I was planning on getting them local to get them as soon as possible.
Old 08-27-2013, 08:10 PM   #13
Hvac Pro
yuri's Avatar
read my post above yours, we sent them at the same time
Old 08-27-2013, 08:10 PM   #14
Thanks!
Old 08-27-2013, 08:12 PM   #15
Hvac Pro
yuri's Avatar
BE careful.
Brayant condensing unit noise MikeKy55 HVAC 1 05-29-2013 11:11 PM
Tempstar DC90 with persistent and annoying clicking noise Carlos245 HVAC 7 11-20-2012 02:10 PM
Rusted and almost gone drain pan, Package unit Nordyne kilosos2 HVAC 3 11-18-2012 10:24 AM
running AC unit off generator hotrod351 Electrical 36 08-19-2012 06:12 PM
Gas boiler vibration & noise when it running Ballastar HVAC 1 05-21-2011 06:00 AM