Clare Furnace Won't Start - HVAC - DIY Chatroom Home Improvement Forum
Old 01-12-2012, 10:12 AM   #1
Clare furnace won't start
I have a clare furnace that will not start. When I turn the thermostat up to call for heat nothing happens. It should start up the vent fan first but it doesn't. If I move the lever from auto to fan the main blower will come on but nothing else. I am not getting any power to the vent fan at any time. It is a natural gas furnace with a s8610u controller
long3817 is offline   Reply With Quote
Old 01-12-2012, 11:17 AM   #2
how
Rewards Points: 1,104
Faulty thermostat, thermostat lines, vent motor, capaciter (if it has one) or board are the most likely causes. Do you have a electrical meter?
how is offline   Reply With Quote
The Following User Says Thank You to how For This Useful Post:
long3817 (01-12-2012)
Old 01-12-2012, 11:35 AM   #3
I'm Your Huckleberry
Rewards Points: 2,270
I went to one yesterday, blower and cool worked from stat but lockout in heat. Carrier. Failed ignitor.
Thanks.
Doc Holliday is offline   Reply With Quote
The Following User Says Thank You to Doc Holliday For This Useful Post:
Old 01-12-2012, 11:44 AM   #4
biggles's Avatar
remove the stat off the subbase and jump W to R don't worry about the settings on the subbase..this should give you a straight heat calll..if nothing again not even the ID motor as you see as the first thing to run the problem is on the control module
The Following User Says Thank You to biggles For This Useful Post:
Old 01-12-2012, 11:44 AM   #5
The vent motor itself is not getting power to it. I have changed the thermostat which has not helped
Old 01-12-2012, 11:46 AM   #6
and yes I have a multimeter. That is how I know it is not getting power.
Old 01-12-2012, 03:14 PM   #7
Check if the limits and roll out switches are closed. If the stat is calling for heat and the safeties are closed but still no power to the inducer motor then it's a control board issue.
The Following User Says Thank You to Marty S. For This Useful Post:
Old 01-12-2012, 05:11 PM   #8
AKA HVACTECHFW
Rewards Points: 1,208
these furnaces were notorious for a failed sequencer that controls the inducer. Last time I tried to get one they were still available but in short supply. ICP (inter city products) now owns that line of parts.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
HEIL gas furnace will not start. Mikeee HVAC 11 01-11-2015 01:35 AM
my bryant furnace 373 does not start carpintero HVAC 1 12-17-2011 09:17 PM
Furnace won't fire, exhaust fan hot and won't start tex800 HVAC 14 10-08-2010 06:48 PM
Oil Furnace Won't start ScottEW HVAC 0 10-05-2010 08:26 AM
Heil furnace won't start - just a click and a hum MrGookat HVAC 4 01-06-2009 07:53 PM