Circulator Pump Is Failing - HVAC - DIY Chatroom Home Improvement Forum
Old 01-29-2013, 05:42 PM   #1
circulator pump is failing
Hi. I have a 900,000 BTU American Standard Boiler from 1939 that had its circulator pump replaced about 5 years ago. The original pump was a Taco 110-24 and the new pump is a taco 007-F5. The new pump is now failing and it has blown its primary overload protector 10 times. Why is this happening? Also the Triple Aquastat Relay made by Minneapolis Honeywell is now clicking like mad.
neo565 is offline   Reply With Quote
Old 01-29-2013, 06:34 PM   #2
An old Tradesmen
Rewards Points: 8,234
A 007 can't move as much water as a 110-24.
900,000 BTUs? Big boiler. What temp are you running the boiler at.
Old 01-29-2013, 07:04 PM   #3
Do you mean the thermostat temp? That is 68 degrees fahrenheit. I cannot see the front of the aquastat due to it facing the wall, 1 foot away from it.
Old 01-29-2013, 07:30 PM   #4
how
Rewards Points: 1,104
Use a mirror to read that aquastat.
Read the 007 instructions to make sure you are installing it in an allowable position.
Check the water you drain off for doing the pump change to see if it's full of debris and the whole system needs flushing..
Consider removing the check valve from the 007 if that's the pump you decide to go with again.
Watch for leaking auto bleeds or relief valves that constantly require the boiler to refill with new oxygenated replacement water which causes faster than normal rusting.
how is offline   Reply With Quote
Failing Capacitor - Why? TipsyMcStagger HVAC 4 10-02-2012 11:38 AM
Panel rusted / corroded & breakers failing stevekem Electrical 25 09-08-2012 02:03 AM
Inducer fan assembly or inducer control circuit board failing realblonde94526 HVAC 3 05-12-2008 07:28 PM
Failing Grout? Ed Coles Flooring 22 04-07-2008 04:43 PM
Floor beam failing? elvinj Building & Construction 8 01-25-2008 01:33 PM