:no:what are the first step to the last step in order form in charging an low charge ac unit for your home properly i just finish hvac school and i didnt learn what i needed from the school because of poor instructor and school thank u
take the course over with another school....better to learn 1st... BEFORE YOU GET IN THE FIELD....NOT TRYING TO LEARN WHILE MAKING MISTAKES AT OTHERS EXPENSE...SORRY....ben sr
nothing good to come of this... i hate to say it but you don't know enough to even be dangerous yet... lock your tools away and go back to school..... or work along side someone.... pay attention and learn
Step 1. Determine if the system is actually low on charge by taking sub cooling and super heat readings.
Step 2. look for leak.
Step 3. Repair leak.
Step 4. Change liquid line filter drier, and vacuuming system.
Step 5. Add proper refrigerant until sub cooling and super heat are at there proper readings.
1. Verify if there is a leak(superheat and subcool) Verifying its not a restriction, dirty coil, air flow issue with duct work.. return ect.. can go on and on (low sub cool and high superheat-leak)
2. Once verified, find leak.. replace or repair .. pull vacumm
3.Determine metering Device and freon type
4.Charge using superheat or subcool(depends on metering device)
5. Some newer Condensors have tags stating what the require depending on outside temperatures
Good Luck.. but school does help before getting on your own!
well if your adding refrigerant one must assume there is a leak or the system was undercharged..