CFM Measurements For Return And Supply Grids - HVAC - DIY Chatroom Home Improvement Forum
Old 09-07-2011, 05:44 PM   #1
JJboy's Avatar
CFM measurements for Return and Supply grids
A/C 2,5T
Return Grid 31x14 (total area)
29x11 (open area) = 2,5 feet x 0.9 feet = 2,250 ft2
1332 CFM
592 FPM
How do I test on the supply? Do I have to measure the area from round duct or the grid?
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 09-08-2011, 02:34 PM   #2
You can use a surface measurement (or slide chart reference available by almost every manufacturer) on how much air can go through the supply registers. That's the same for ducting, usually that is in a wheel form for flex.
Is that a vane ammeter? You can do a quick check that will "ball park" your cfm to a zone. This is typically what inspectors will do.
To get a true reading you will also need to dig deeper into this with a tube reader in each branch of the supply ductwork.
Ultimately it's two things that really matter;
1. Cfm at the supply
2. Overall static pressure
Dr.HVAC is offline   Reply With Quote
Old 09-08-2011, 03:37 PM   #3
Experienced
Jackofall1's Avatar
Originally Posted by JJboy View Post
A/C 2,5T
1332 CFM
592 FPM
JJ--
29x11 = 319 in2
319/144(in2 per 1 ft2) = 2.215 ft2
You would then have to apply a "K" factor for the grill say .8
So
2.215 x .8 (K Factor) = 1.77 Ft2
1.77 Ft2 x Velocity = Volume
You can apply the exact same principle to the supply air registers and then total the supplys up.
You will also need a slack tube to measure static pressures in the system.
Keep in mind that the accuracy of a vane anometer is less than 90%.
Mark
Old 09-08-2011, 04:51 PM   #4
JJboy's Avatar
CFM at the supply = Velocity x area of the supply grid - How to I know if duct is correct?
Overall static pressure:
Can I use digital manometer at return and supply ?
Old 09-08-2011, 05:06 PM   #5
JJboy's Avatar
Originally Posted by Jackofall1 View Post
JJ--
29x11 = 319 in2
So
Mark
So If I don't have the K factor the area will be:
(29x11)/144 right?
If I have the K factor the area will be:
{(39x14) x K factor }/144 right?
Can I use my digital manometer to get static pressure?
Old 09-08-2011, 05:25 PM   #6
Sounds ok to me, again, check for the resistance levels from the mfg. Assumptions make the whole process a time consuming guess.
I use a u tube. I have had a few digital manometers but still feel a more accurate constant on the liquid tube (the internals of an old diaphragm just sketches me out)
Technically, static pressure is made of averaging several measurements on the supply/return side....I do mostly residential and am fairly happy to get three that are decently spaced from the equipment.
Testo has some good videos on how to use their products on trunks for accurate readings (I haven't looked, I bet they're on YouTube)
Hope that helps
Grossly insufficient water supply to toilet wasting water? mysterylectric Plumbing 8 01-17-2012 11:19 AM
Distance between HVAC supply and return vents atlantatd HVAC 4 04-13-2011 08:30 PM
Need help fast please re hydronic boiler water supply and backflow DanDaMan HVAC 6 12-11-2010 02:26 PM
Supply valve to bath faucet doesn't stop water Kurt123 Plumbing 2 09-05-2010 09:48 PM
Extending Water Supply Box In Laundry Room hsl Building & Construction 0 11-18-2009 09:21 AM