Central Air Condenser Disconnect - HVAC - Page 4 - DIY Chatroom Home Improvement Forum
Old 04-25-2012, 06:43 AM   #46
Rewards Points: 582
why can't we all just get along ok signing off enjoy guys...
Old 04-25-2012, 08:19 AM   #47
Originally Posted by Skelleyman View Post
Hello All,
I'm a DIY'er for most things except things that I want perfectly done and I know my limits. My brother is a licensed Master electrician but has really only dealt with Commercial last several years - his company are commercial electricians who setup new building contruction etc..
Anyway, my wife and I are getting Central Air from our tax money this year. That project starts in two weeks. My brother is going to tie everything together for me (electrical) but I had to do the research and buy everything. The HVAC installer said I need a 30A 2P GFI breaker to a 30A disconnect on the side of my house. I have the breaker specific to my panel, 10-2 wire and PVC conduit, etc.
Question:
I did purchase a 30A fusible pull-out disconnect box and 2x 30A NOS type H fuses. Will this work? The condenser is a new Trane XB13 and I can't find any documentation stating it needs fusible over non-fusible.
Thanks,
~S
Use a simple disconnect, not a fuse or breaker.
Each fuse or common breaker (thermal) introduces a voltage drop since they use resistance to generate the heat to blow or trip. This wastes power and lowers voltage to the AC, thus it's performance however slightly.
Actually, buried in the NEC there is a limit on how many current limiting devices can be in some circuits just for this reason.
gerry
gerry_g is offline   Reply With Quote
Old 04-25-2012, 09:50 AM   #48
~snicker*chortle~
hvac5646 is offline   Reply With Quote
Old 04-25-2012, 03:40 PM   #49
newtech's Avatar
Rewards Points: 164
Originally Posted by COLDIRON View Post
Removed text not needed for reply....
So your reply was ???
newtech is offline   Reply With Quote
Old 04-25-2012, 05:21 PM   #50
Rewards Points: 1,216
"The only reason heater overloads are installed on large equipment is if the temperature goes below 32 deg". You asked.
COLDIRON is offline   Reply With Quote
Old 04-26-2012, 02:53 PM   #51
newtech's Avatar
Rewards Points: 164
The three "opposed-question-mark" shaped devices in series with each phase going to the motor are called overload heaters. Each "heater" element is a low-resistance strip of metal intended to heat up as the motor draws current. If the temperature of any of these heater elements reaches a critical point (equivalent to a moderate overloading of the motor), a normally-closed switch contact (not shown in the diagram) will spring open. This normally-closed contact is usually connected in series with the relay coil, so that when it opens the relay will automatically de-energize, thereby shutting off power to the motor. We will see more of this overload protection wiring in the next chapter. Overload heaters are intended to provide overcurrent protection for large electric motors, unlike circuit breakers and fuses which serve the primary purpose of providing overcurrent protection for power conductors.
Overload heater function is often misunderstood. They are not fuses; that is, it is not their function to burn open and directly break the circuit as a fuse is designed to do. Rather, overload heaters are designed to thermally mimic the heating characteristic of the particular electric motor to be protected. All motors have thermal characteristics, including the amount of heat energy generated by resistive dissipation (I2R), the thermal transfer characteristics of heat "conducted" to the cooling medium through the metal frame of the motor, the physical mass and specific heat of the materials constituting the motor, etc. These characteristics are mimicked by the overload heater on a miniature scale: when the motor heats up toward its critical temperature, so will the heater toward its critical temperature, ideally at the same rate and approach curve. Thus, the overload contact, in sensing heater temperature with a thermo-mechanical mechanism, will sense an analogue of the real motor. If the overload contact trips due to excessive heater temperature, it will be an indication that the real motor has reached its critical temperature (or, would have done so in a short while). After tripping, the heaters are supposed to cool down at the same rate and approach curve as the real motor, so that they indicate an accurate proportion of the motor's thermal condition, and will not allow power to be re-applied until the motor is truly ready for start-up again.
Never heard the 32 deg factor. I see them all the time even when there is no way in h*11 that the space would ever reach 32 deg.
Just sayin
Old 04-26-2012, 04:59 PM   #52
Come on New You can't tell I was being a wise guy ? Your slipping.
Wow I thought you knew me better than that. 32 degrees has nothing to do with equipment heaters. Heaters are as described in your post and are sized by charts by each manufacture and equipment requirements.
Old 04-26-2012, 06:38 PM   #53
Just sayin
cut and paste?
Old 04-26-2012, 08:09 PM   #54
Rewards Points: 582
Originally Posted by hvac5646 View Post
cut and paste?
Old 04-27-2012, 03:44 AM   #55
newtech's Avatar
Rewards Points: 164
Sorry, had one toooo many ginger ales when I posted it
Central Air Condenser Disconnect Skelleyman Electrical 15 04-21-2012 11:15 AM
Installing central air question about conduit from disconnect to panel angelas111 Electrical 2 05-27-2011 07:37 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
wiring my condenser fan to my central air unit 45lonnie Electrical 1 09-05-2010 09:52 AM
Moving condenser electrical disconnect, required? Dave Carney HVAC 7 07-27-2009 10:34 PM