Carrier Weathermaker 9200 - HVAC - DIY Chatroom Home Improvement Forum
Old 01-18-2011, 06:54 PM   #1
I have a carrier weathermaker 9200 it heats the house fine. However when it is running it shuts off and starts back up again, is this normal? Also you can hear water gurgling outside the exhaust vent. Any ideas? I have sucked out the vent with a shop vac and pulled maybe 12 oz of water out of it. The drain lines are all clean and clear. Any help would be greatly appreciated.
klrz28 is offline   Reply With Quote
Old 01-18-2011, 07:05 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,424
Make sure all the exhaust piping is sloped back to the furnace properly and has no sags in it which will collect water. Then it backs up and blocks the pipe and starts tripping a pressure switch. Add more hangers with perforated nylon coated strapping if necessary.
Old 01-20-2011, 08:35 PM   #3
I fixed the pipe issue no more gurgling. All though the furnace still continued to shut off and on while heating, so I cut in a extra cold air return vent and went with a thinner furnace filter. The heat exchanger was getting too hot and shut down, problem solved, Thanks,
Old 01-20-2011, 08:45 PM   #4
Hvac Pro
yuri's Avatar
Glad to hear you got it going. We don't always get the positive results/outcome here.
Old 03-09-2011, 07:42 PM   #5
Now its having a issue with staying running. It fires up runs for a few minutes then the burner shuts down, blower cools down the heat exchanger then shuts off and then fires back up again. Flashes 33 is there a bad sensor? What can it be? Is it getting too hot? Not enough cold air return? Weak blower motor? A coil is clean. What can it be?
Old 03-09-2011, 08:27 PM   #6
Rewards Points: 380
Have you tried a temperature rise test accross the heat exchanger to see if the unit is actually overheating or if you have a bad limit switch? Take a thermometer and check the discharge air temp and then check the temp. in the return air duct and calculate the difference, then check the rating plate inside the furnace for the heat rise (it will be a range) (typically 40-70 degrees F) and see if you are in that range. If you are outside (above the range) in temp. difference then you have an airflow issue and the furnace is in fact overheating. Have you by chance been running it without a filter for a period of time? If so you may have a restricted secondary heat exchanger which can plug up just as you suspected your A/C coil may have been. If this is the case, you must remove the blower assembly and sqirm in on your back and look up to the heat exchanger and see if it is restricted and clean that coil if it is.
HVACDave is offline   Reply With Quote
Old 03-09-2011, 10:13 PM   #7
The heat exchangers look clean. This house is on a crawlspace. The crawlspace walls are insulated. the duct work is insulated as well. Should I remove the insulation from the ducts to help disperse the heat from the trunk? I am almost positive its the limit switch tripping from excessive heat.
Old 03-10-2011, 10:00 PM   #8
Or Can I add a duct and Bring in Fresh air from the outside of the house to help, maybe add a damper to it to adjust air flow coming in? I know most homes air inside the home is 4-5 times dirtier than the outside air. Any thoughts are greatly appreciated.
Old 03-11-2011, 04:32 PM   #9
Rewards Points: 380
Has this been an ongoing problem, or has it become more noticable just lately? How large is the furnace (btu's) and how much ducting do you have connected?
Old 03-11-2011, 09:27 PM   #10
I believe its been doing it for some time just haven't noticed.
Old 03-11-2011, 09:28 PM   #11
I believe its a 80,000 btu
Old 03-11-2011, 09:29 PM   #12
I believe there is 13 supply ducts and 7 cold air ducts.
Old 03-29-2011, 12:10 PM   #13
It has to be starving for cold air. If I take out the .99 cent air filter and leave the cover off it will run all day long and not hit the high limit. So it has to be starving for more air. The furnace is up side down. The cold air return is on top of the furnace and pushes the heat down under the house thru the trunk. The a/c coil is clean. So now I dont know what to do to get more air to it. There already is a Cheater duct above the furnace that seemed to help a little but its still not enough air. One other thing. All of the crawlspace perimiter walls are insulated and visquine is laid on the floor.
Old 03-29-2011, 12:20 PM   #14
HVAC / Plumbing
Hard to believe that a new 99 cent filter is enough restriction to limit air flow.Duct must be way undersized. Are all the return vents clear / have no restrictions ?
kenmac is offline   Reply With Quote
Old 03-29-2011, 12:28 PM   #15
The previous owners had the 4 inch thick filter in there and I noticed it hitting the high limit. It would shut down and fire back up. I think the furnace is too many btu's for the house. Im no hvac expert.
Carrier Weathermaker 9200 - Blower not turning on. bvijay HVAC 7 08-15-2011 08:04 PM
Carrier weathermaker 9200 jnspence HVAC 3 12-07-2010 12:37 PM
Carrier Weathermaker 9200 for LP/Nat? 1Mike HVAC 7 07-01-2009 09:02 AM
Trouble Shooting a Carrier 9200 Weathermaker Furnace JoeDell HVAC 4 01-08-2009 05:07 PM
Problem with Carrier Weathermaker 9200 Chipley HVAC 12 12-16-2008 01:44 PM