#1 |
Carrier Weathermaker 8000 not lighting-please help!
We have a Carrier Weathermaker 8000, model # cb5axa030000aaaa. When we turned on the furnace, it would not light. I took out the hot surface igniter and it was white so I got a brand new one, factory direct to replace it. The HVAC guy at the supply store told me not to tough it to anything when replacing and I did not, however, it is still not lighting.
If you turn on the furance, I can hear the fan going on, then the motor and I can hear the click but the igniter is not glowing and no flame. Though it sounds like it is running. What might be the problem? Thanks for your speedy help! It is chilly in here. Karyn |
#2 |
You'll need a multimeter to check if the ignitor is getting voltage and to see if the low voltage safeties are closing.
#3 |
My husband has a multimeter, where exactly would he need to check for voltage and the voltage safeties?
Thank you for your response. Karyn |
#4 |
Check also pressure switch
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead. |
#5 |
where would I find a pressure switch?
#6 |
#7 |
what code is it giving you
#8 |
we do not have a LED code display on our furnace. My husband was testing the circuit board and it appears that it might be the hot surface ignition relay. He has a call into a local service and hopefully we can pick up a new board tomorrow. In the meantime, we will be in layers tonight-house is down to 60*.
#9 |
ok, so now we have a new board in there, and it is showing code 12 and then 13, sometimes 33. in the upper right hand, I believe is the pressure relay. He tested with a meter and the in voltage is about 26 and the voltage coming out is about 9. Thoughts?
Oh I hope we fix this soon. 56* inside in Michigan is not fun. Thanks for any help |
#10 |
The 13 and 33 are limit switch indications I believe. Check on the inside of the doors for the furnace. On one of them you should have a listing of the code faults and what they mean. Unless your original furnace didn't have that kind of control board.
#11 | |
Carrier Weathermaker 8000 not lighting-please help!Quote:
| The Following User Says Thank You to Marty S. For This Useful Post: | carmon (10-31-2012) |
| Tags |
igniter not glowing ![]() |
| Display Modes | |
| Carrier Weathermaker 8000 help | moose404 | HVAC | 2 | 03-13-2012 09:11 AM |
| Carrier Weathermaker 8000 thermostat out, air blowing | Saveme$ | HVAC | 30 | 01-08-2012 11:42 PM |
| Carrier Weathermaker 8000 | Deisic | HVAC | 0 | 08-16-2010 10:15 PM |
| Carrier Weathermaker 8000 help please | TenTwelve | HVAC | 2 | 01-11-2010 06:49 PM |
| Carrier Weathermaker 8000, Gas Furnace Problem | kiss44 | HVAC | 1 | 10-18-2009 09:27 AM |