Old 09-20-2011, 08:41 PM   #16
Carrier heatpump, when in AC the blower is not turning off
JJboy, that is the board. My hvac buddies where telling me to change the board. I'm on the same page here with you, I don't think it can be the board, since there is really nothing there to go bad, no dark burn marks or any sign something has burnt. So I think I've eliminated the thermostat which leaves on thing, the module on the back of the motor. Grrrrrrrr, mine happens to be an odd-ball RMOD44AE119. Very few sources and quit expensive.
Does that make since to you?
metalmover is offline   Reply With Quote
Old 09-20-2011, 08:46 PM   #17
Ok..so you have a variable speed then.
The blower doesn't need a call on g to run. It will run on the Y signal. There is a cooling fan delay jumper on the board. I would move it to enhanced (enh).
Master of Cold is offline   Reply With Quote
Old 09-20-2011, 09:03 PM   #18
Originally Posted by Master of Cold View Post
If you can post a pic of what control board you have it would make it much easier. You are saying "ecm" motor. But if this is a variable speed blower there is not a problem, just a fan delay timer that can be adjusted..
JJboy posted the board. The blower motor has a housing with control module on the back look like this
The second level, that you cant see has small coils and memory chips or e-proms.
Old 09-20-2011, 09:06 PM   #19
Yes it variable speed. If you post a pic of the board so we can see the jumpers and tell you where to put them.
Old 09-20-2011, 09:26 PM   #20
There is a grey wire that is on the 90/0 terminal now. Which in the pic is the left side terminal, I see enhanched on theright
here's the board
Old 09-20-2011, 09:38 PM   #21
JJboy's Avatar
Maybe this help.
http://img822.imageshack.us/img822/3287/modulei.jpg
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 09-20-2011, 09:48 PM   #22
I'm Your Huckleberry
I have some kind of ecm variable speed tester thingamajig. I think you simply hook it up low voltage straight to the motor and control it on and off as such, bypassing in house control wiring.
I've never used it to date so not really sure, it's just collecting dust in the truck.
Doc Holliday is offline   Reply With Quote
Old 09-20-2011, 10:00 PM   #23
Top slot is auxillary heat size. It should tell the kw on heater plate
Next slot is condenser size-look on condenser for model number if it is still there
Set the next one for heat pump -eff
Next set cfm at low
Lastly set for enh(anced)
Old 09-20-2011, 11:53 PM   #24
Next set cfm at low
You my friend are THE MAN!
They where all hooked up wrong except for CFM. The installer just went to the first pin on the right and hooked them up. (board is upside down) What an idiot!
Only one I'm not sure of is the condenser hp, I'll pull the cover off in the morning and get that.
The AC fan still will not cycle off, wonder if the incorrect hook up has screwed something up in the fan control?
I need to look at the thermostat wiring also.
Thank- you!!!
Old 09-21-2011, 12:50 AM   #25
Checked the thermostat wiring at the board, the O wire was hooked to Y/Y2. Changed to O to O and the darn thing works perfectly! SOOO much quieter in AC mode!
I am jumping up and down yelling "it's fixed!"
Master of cold, I can't thank you enough! You saved me hundreds of dollars and a whole bunch of aggravation!
You ever come to Virginia PM me, I'll hook you up with a couple of tickets to Busch Gardens.
Bob
Old 09-21-2011, 07:55 AM   #26
Not a problem..glad to help.
Bryant Plus 90 - No Blower Ducaticorse HVAC 11 10-16-2012 09:39 PM
Carrier Weathermaker 9200 - Blower not turning on. bvijay HVAC 7 08-15-2011 08:04 PM
Carrier 58MXA Wiring Blower Switch 63012753 HVAC 0 10-06-2009 10:09 PM
Carrier 58SX Main Blower Turns On Without Command otismyman HVAC 19 09-25-2009 08:06 PM
carrier blower not turning off agartin HVAC 12 10-12-2008 12:42 PM