Split 10 ton carrier. The Mayor got an electrician to replace the t-stats in town hall. Ive replace 4 75va trans. and rewired all stats, BUT this carrier 38AQ012500 will not shut down when the t-stat is satisfied. The indoor blower stops but the condenser keeps running. Take the reversing wire off and it stops, put it back on and it starts!! any suggestions?
ridgevilleac is offline   Reply With Quote
Old 11-09-2010, 06:53 PM   #2
HVAC / Plumbing
Sounds like someone didn't wire it correctly
kenmac is offline   Reply With Quote
Old 11-09-2010, 07:03 PM   #3
Duh ya think? Ive wasted several hours trying to figure this one out. Defrost timer is the old style but nothing stuck. Its got to be a stuck relay somewhere but WHERE?
Old 11-09-2010, 07:21 PM   #4
An old Tradesmen
Rewards Points: 6,592
How many thermostats are controlling this 1 unit?
Is it a zoned unit?
Old 11-09-2010, 07:26 PM   #5
1 t-stat Honeywell 6000 electronic. O energizing W1 on condenser.
Old 11-09-2010, 07:26 PM   #6
Not zoned
Old 11-09-2010, 07:48 PM   #7
An old Tradesmen
Ok. You threw me of. When you said you rewired all thermostats.
What terminals does the outdoor unit have. Carrier RTUs(newer ones) don't use an O terminal anymore. But split units do.
Old 11-09-2010, 08:38 PM   #8
They screwed up more than this one. TB is top to bottom R, Y1, Y2, W1, A2, X, C, P
Old 11-09-2010, 08:51 PM   #9
An old Tradesmen
Just connect the W1 of the stat to the W1 of the outdoor unit. Don't use the O.
Old 11-09-2010, 09:30 PM   #10
Which de energizes the reversing valve.... Thank You!!
Old 11-09-2010, 09:37 PM   #11
Makes perfect sence!~ I was litterally pulling my hair out with this. Don't know why I did'nt think of that. geesh Thank you-Thank you-Thank you!
Heatpump vs Natural Gas - Energy Cost Spreadsheet zootjeff HVAC 11 06-22-2015 04:59 AM
Help with Heat Pump System Wiring AlanScott HVAC 11 10-10-2010 01:19 PM
Getting a House..heatpump or no? DavidsCPU HVAC 10 02-07-2010 11:22 PM
Which diagram to use on Lenox Thermostat wiring setup? Heat Pump Lenox techs needed twilightcall HVAC 1 08-13-2008 12:49 PM
Carrier Infinity T-stat and Performance heat pump gcole HVAC 3 10-03-2007 04:00 PM