Old 11-05-2007, 08:46 AM   #1
Carrier Gas Furnace 58MXA080
my fan ran all the time during summer so I just replaced the tstat a couple of weeks ago.
Now when I turn the heat on ... there is none. Again, fan runs all the time. On the LED it starts off with code 33 and then goes to 13, as advertised.
Kinda lost from here, the reset does not seem to do anything. Should the heat be "running" when I try to do the reset?
Any ideas what the problem could be here?
fredfillis is offline   Reply With Quote
Old 11-05-2007, 04:23 PM   #2
FWIW, The tstat I used was a Hunter Autosaver 550
I've run the "diagnostics". According to the service manual, I disconnect the R terminal on the control board and then short the Test terminal to the Com. LED is supposed to go out, mine just flashes quickly. When I remove the short it goes back to Code 33.
Old 11-05-2007, 06:20 PM   #3
Thoroughbred Mopar Man
Hi fredfillis
I would say that you have an open limit. Look on the back of the front panel of the furnace. On it you will see a legend that will tell you what each of the codes mean. I would venture to say you have either a rollout limit tripped or the vestibule limit is bad. If you have a voltmeter, turn the thermostat to the heat mode and check for voltage across the limits. If you show voltage at any one of the limits, that limit is open. Some of them have a reset button between the wires. However the vestibule limit does not, it is a automatic reset that has about a twelve trip life. If it is bad, I would reccomend checking the evaporator for blockage of air flow or use a better grade filter. Hope this helps, let us know if we can assist any further.
Good luck
Rusty
Character is doing the right thing even when no one is looking. Intelligence is understanding and practicing the meaning of character.
#CARRIERMAN is offline   Reply With Quote
Old 11-05-2007, 06:42 PM   #4
Thanks Rusty. I'll do those tests tomorrow. If the vestibule limit is bad, is it replaceable?
Old 11-05-2007, 06:58 PM   #5
Hi fredfillis
Yes the vestibule limit is replaceable. As with any electrical component, shut the power off. This limit is in the middle of the furnace, its dimensions are about 2" wide by about 3 1/2" high. It will either be black, brown, or a beige color. They usually run about $12.00 to $25.00 dollars.
Good luck
Rusty
Old 11-06-2007, 04:25 PM   #6
Both limits check out correctly. No voltage across either. Both measure less than 2 ohms. Both show 26v to ground.
Just for fun, I pulled the wires off each and shorted them, started the furnace and got LED codes 33 then 13 just as before. I'm thinking control board.
Old 11-09-2007, 06:47 PM   #7
New control board and all is well.
More On This Topic
If your appliance is not working properly and has a split phase motor, you may be able to repair the problem yourself. Resolving the problem with your split phase motor can be fairly easy once you determine what the problem is. Read More »
Hello! This is Ross on behalf of expertvillage.com. How do you measure voltage in a circuit? You have a circuit. It is not powered up yet the LED is off and go ahead and apply the positive to the circuit or you have the negative from my power supply... Read More »
Hello. This is Jeff Naylor from Mtroniks Engineering in Mesa, Arizona for Expert Village. Now that the tubes are warmed up, we're going to bias them using the current method. Connected to the cathode of the tube to ground, there's a one resister. If we... Read More »
Hello! This is Ross on behalf of the expertvillage.com. What happens to resistors in terms of value of resistance in a series circuit whenever series is the one connects after the other. So if we have the second resistor what happens the resistances add... Read More »
Hello. This is Jeff Naylor from Mtroniks Engineering in Mesa Arizona for Expert Village. Leaving our black, negative lead connected to the center pin, we are going to switch our positive voltmeter lead from the left most pin to the right most pin. This... Read More »
Carrier furnace help code 13 mudtruck HVAC 5 04-08-2008 11:47 PM
carrier furnace issues sbroways HVAC 2 10-15-2007 09:30 PM
Putting a new Motor in a Carrier Furnace... Wiring issues cbrent HVAC 3 10-08-2007 07:08 PM
My Carrier furnace is driving me crazy hifiuser HVAC 6 02-10-2007 10:48 AM
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.