Old 04-17-2011, 09:55 AM   #1
Carrier furnace not igniting-bad control board?
I have a Carrier 58mca furnace with a HK42FZ016 control board. It flashes code 24 when no call for heat is active then flashes code 21 once a call for heat is initiated. The inducer motor and blower start up but the ignitor never glows to ignite burners. I have checked the 24 vac is properly supplied from the transformer. I attempted to run a component self test but it will not run. If I keep the test/twin shorted to common it does flash the LED rapidly recognizing the attempt. Thoughts on where to proceed to next?
Thanks!
-Wes
stick_boy1106 is offline   Reply With Quote
Old 04-17-2011, 10:51 AM   #2
Hvac Pro
code 24 is secondary fuse blown. should be a 3 or 5 amp plastic gm auto fuse on the circuit board. if it blows again then you have a short in the wiring.
Old 04-17-2011, 10:59 AM   #3
I checked the fuse and it is not blown. I also disconnected all the thermostat wiring from the control board and the code 24 remained.
Cheers,
-Wes
Old 04-17-2011, 11:01 AM   #4
Hvac Pro
Probably a bad circuit board as it is giving false readings. Should not give the 2nd code as it cannot initiate a call for heat with a blown fuse. Try americanhvacparts.com for carrier parts
make sure you have a proper 120 volts to the furnace. 120 from hot to ground not neutral, 0 from neutral to ground and continuity from the green ground wire to a copper water line. use a cheater wire from water line to your meter if necessary. if you have reversed polarity or a bad ground or neutral it can give false readings. rare but possible.
Old 04-21-2011, 07:28 PM   #5
Retired Electrician
try ebay i bought newboard replacement for $99
fy171 is offline   Reply With Quote
Universal furnace control board Davidj0717 HVAC 1 10-14-2009 06:37 PM
Goodman 4 flashes on control board bigmac71201 HVAC 6 09-28-2009 03:53 PM
carrier furnace and honeywell zone control issue bmccarron HVAC 14 09-20-2009 10:59 AM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM
Ruud a/c control board replacement ? kourso HVAC 1 07-20-2006 10:33 PM