-   -   carrier furnace and honeywell zone control issue (http://www.diychatroom.com/f17/carrier-furnace-honeywell-zone-control-issue-53290/)
bmccarron 09-18-2009 11:14 AM
Hello all, first time poster here and hoping someone can offer some guidance. I have a Carrier AC and Furnace (model 58STA090-10116. Manufactured in December of 2003) in my home. One of my neighbors has his own heating and air business and I had him split my system into 2 zones. One upstairs and one Downstairs. It is working great except for one small thing that he and I cant seem to figure out. He said he was going to get some opinions from some other ac guys and get back to me, but I figured I might work it on my end too. It operates fine until after the a/c call is done. The purge cycle begins and then the fan runs for about 90 seconds, there is a clunk (and the air flow decreases for a second) and then it runs for about another 30 seconds and shuts off. It seems it is running high speed for the first 90 seconds as the furnace does by defaut for a purge after an ac call and then reverts to slower fan only speed for the remainder of the zone controls 2 minute purge cycle. Someone had suggested that the j2 jumper on the control board needs to be clipped for it to work properly, but I wanted to confirm that prior to doing so. Does anyone else have any ideas? Thanks for any help you can offer!
beenthere 09-18-2009 12:17 PM
If we knew which Honeywell zone panel that would help.
bmccarron 09-18-2009 02:05 PM
sorry i made sure i put the furnace model in and totally forgot the zone control. it is a emm-3
Flashheatingand 09-18-2009 04:24 PM
What I believe is happening is that the control board now gets it's signal from the zone board as opposed to the t-stat. As a result, the zone board is doing a delay on break first. Then, the control board on the furnace is doing a delay on break. I am not certain if you can get rid of the "d.o.b" with the zone board, but it is likely that you there are dip switches on the furnace to alter the d.o.b. with it's control board.
beenthere 09-18-2009 04:36 PM
Not aware of that panel being able to have the purge overrode by cutting a jumper.
I could be wrong though.
Your furnace may have an adjustable "fan on" blower speed. If so, your contractor can adjust that, and probably eliminate the noise.
Or, he may be able to increase the furnace blower delay off time, to march the zone panel.
Flashheatingand 09-18-2009 09:16 PM
The thing is that the zone board sends the signal to the furnace control. I think the simple thing to do is to wire the y from the zone board to the y/contactor lead. When the furnace board gets 24 v at the y terminal, there is blower off delay. Change the dip setting to no delay, or by-pass the furnace board. That way, it wont get the y signal.
I can be wrong, but based on the reading only, My bet is that is where the problem is. But that is just internet talk.
beenthere 09-18-2009 09:38 PM
If the board doesn't get a Y signal. then the blower won't go to cooling speed. And the evap coil could freeze.
Plus. It will still have a delay off on a heating call.
Flashheatingand 09-18-2009 10:10 PM
Maybe you can turn off the furnace delays altogether. One could deal with the cooling fan speed thing if necessary, but something needs to be done about the heat delay. Either way, something needs to be done about that short cycle. Offhand, I don't know how to override the purge, unless you wire a push button switch at the living room coffee table.
bmccarron 09-19-2009 12:06 AM
As far as I can tell, the blower off time for a cooling call is not adjustable, on either the zone control or the furnace
furnace install guide
http://www.docs.hvacpartners.com/idc.../58st-19si.pdf
zone control
http://customer.honeywell.com/techli...it/68-3041.pdf
Can you tell i have been looking at this for a while?
Flashheatingand 09-19-2009 10:18 AM
I took at look at the material you just posted. Look at page 24 on the furnace document. you will see some dip switch settings at the 12:00 postition on the control board. There is something there to deal with the blower delay.
bmccarron 09-19-2009 11:28 AM
Yes I see that, but that only deals with the heating delay not the cooling. See page 50 and tell me what you think
beenthere 09-19-2009 12:11 PM
Cutting that jumper will probably just get you the noise sooner.
Ask your contractor what the temp rise is in heating mode.
It may be high enough that he can make heating and cooling speed the same. If he can, that will eliminate the noise.
bmccarron 09-19-2009 12:21 PM
Is it possible on this unit to make them the same speed?
beenthere 09-19-2009 12:28 PM
Yes.
Just need to disconnect one of the 2 current speed taps. Cap it or park it. And run a jumper from that board terminal to the other terminal.
Then when either mode is called for, it runs at the same speed.
Flashheatingand 09-20-2009 10:59 AM
You probably have figured this out by now, but. The zone board and the control board are both doing a purge. Unfortunately, the zone board does a purge at the lower speed, while the furnace purges cooling at a higher speed. Don't cut the j2 wire,
Two possible solutions. One is to remove the cool speed tap and jumper that speed with connection with the heat lead and use whichever wire is more appropriate (I would think the lower speed would be the first choice). Pretty much what Beenthere stated previously.
Another measure you can take which I believe, will pretty much do the same thing, is to remove the wires at the y terminal on the furnace board and wire-nut them together. Doing the jumper thing isn't rocket science, but you will need certain hardware, or need to cut wires...etc. It's just that taking off the wires is a less time consuming, and you can always put it back.