Carrier Furnace Burners Cycling On/Off - HVAC - DIY Chatroom Home Improvement Forum
Old 10-15-2012, 02:16 PM   #1
Furnace: Carrier 58GP150-LA Upflow (about twenty years old with match lit pilot)
Last week I turned on the furnace and experienced the following problem. Thermostat calls for heat, burners fire up, blower turns on approximately 90 seconds later.
After a few minutes of operation, the burners turn off, fan continues to run for several minutes and turns off. Pilot light stays on and seems to be fine.
Immediately after the blower turns off or concurrent to turning off, I hear a click (from HFR relay?), burners fire up and cycle repeats. This continues until the thermostat setting is reached.
Checked resistance across fusible link connected to limit switch terminal - 0 Ohms.
Put the ohmeter across limit switch and noticed that it goes high when burner turns off.
Connected a jumper across limit switch terminals and furnace resumed normal operation until Tstat setting reached. Concluded the LS was likely the problem as a couple of years ago the blower ran continuously with out burner and tstat off. Tapped on the LS to check it and it started working again fine with no problem until now.
Ordered a new limit switch. Tried to solder on the old fusible link to the new LS terminat and unfortunately it burned out. Nevertheless, since it was good before, went ahead and installed the new LS this morning without a fusible link (Iíll buy it later since Iím confident there shouldnít be a flame rollout problem). Fired up the furnace and the exact same problem occurs again.
So what could it be if not the LS? Schematic in the ownerís manual shows Blocked Vent Shutoff Switch (BVSS) which must be reset if it triggers according to manual, so canít be a blocked vent?
So now Iím stumped. What else could be causing these symptoms? Something causing the gas valve to de-energize but what? Pilot light seems fine. Could the furnace be overheating and if so, what could be causing that.
Any suggestions on how to proceed next will be appreciated. Thanks.
diyguy777 is offline   Reply With Quote
Old 10-15-2012, 03:03 PM   #2
HVAC Tech/Owner
Rewards Points: 604
Low airflow
Technow is offline   Reply With Quote
Old 10-15-2012, 05:21 PM   #3
I enjoy helping the DIY crowd on here but in this case it's time to stop and call a pro. Leaving the roll out off on a 20 year old furnace clearly shows this job to be beyond your ability to work on a furnace safely. Sorry to be a stick in the mud but it needed to be said.
The Following 2 Users Say Thank You to Marty S. For This Useful Post:
ben's plumbing (10-15-2012), hvac benny (10-15-2012)
Old 10-15-2012, 07:23 PM   #4
Rewards Points: 582
agree with technow maybe the limit switch is doing its job.....opening up on tempeture rise....check air flow ...filters,,blower..coil if is has a/c...go from there..ben sr
Tags
burner , bvss , fusible link , limit switch
Natural Gas Cost For Furnace 1 Hour Run Time hammerlane HVAC 25 01-14-2015 03:13 PM
Luxaire Gas Furnace - Short Cycling dvan76 HVAC 14 10-31-2011 01:47 PM
Carrier Cobra Gas Furnace Problem carriercobra HVAC 13 12-30-2009 12:47 PM
Carrier Furnace Problem... cornation71 HVAC 3 12-10-2009 08:52 AM
Zoning With Carrier Infinity Furnace ddartmouth HVAC 1 01-05-2009 12:55 PM