Old 12-09-2011, 11:49 AM   #1
Carrier Furnace (1985) No Pilot
The paperwork I have on this furnace says it's a 58SE but the illegible model number begins with a 394.
Sometimes the pilot will light and the furnace will operate properly. More often the pilot will not light and obviously the furnace will not heat. I have electrical knowledge in automobiles but not in HVAC. All my lne voltages (120) and transformer (28) voltages appear to be correct. I'm not too sure how to check for proper voltages at the pilot
What I am experiencing is the electric starter not clicking/sparking to start the pilot. I tapped the pilot a couple of times and it began working. When the pilot lights, the furnace seems to operate properly. It has a 3 wire pilot. For lack of knowledge of the sequence of events, I installed a new control board with no change inn the way it currently operates.
One other thing I notice is when the fan is turned to on at the T/stat, the fan will not run but it does run when the pilot has lit and furnace is heating up.
Thanks.
Don
tlc4dna is offline   Reply With Quote
Old 12-09-2011, 01:16 PM   #2
biggles's Avatar
that ignitor is looking for a ground make sure all is clean and no rust in or on the pilot assembly sand paper the area just opposite the ignitor rod check the ead to ground off the module should see voltage going out thru the orange wire to the rod... hitting it and it sparked and lit sounds like rust or loose grounding around the pilot assembly not different then the cars plugs with a solid ground
Old 12-09-2011, 04:20 PM   #3
Thanks. I will clean it up and recheck it after work today.
Old 12-09-2011, 04:48 PM   #4
I'm Your Huckleberry
Pilot or spark ignition? Two entirely different things.
Doc Holliday is offline   Reply With Quote
Old 12-09-2011, 06:01 PM   #5
I'm guessing spark ignition. It has a small black high voltage module and a silicone shielded wire running to the pilot. It sparks to light the pilot.
Is there a test for the spark/high voltage module? It has 28 volts to it.
Old 12-09-2011, 06:10 PM   #6
Houston204's Avatar
I don't see a Carrier 394. Could it be a Bryant?
Houston204 is offline   Reply With Quote
Old 12-09-2011, 06:22 PM   #7
Houston204's Avatar
This is a Carrier 58SE manual with 3 wire ignition...
http://www.docs.hvacpartners.com/idc...t/58se-3si.pdf
Old 12-09-2011, 08:04 PM   #8
Ok, my bad. My paperwork says it is a 58SC not SE as I wrote earlier. It looks like the 58C not the Bryant. This model does not have a draft inducer motor on it. The only markings on the front are Day/Night
I removed the pilot and cleaned the mating surfaces as well as the spark surfaces. When I turn it on, I can hear the gas and I got one spark then it quit. I have voltage to the spark ignitor and I have continuity all the way to the electrode but no spark.
Is there a way to test the spark ignitor?
Old 12-09-2011, 09:52 PM   #9
Change the ignitor first.
New Carrier Furnace and A/C OmahaGirl HVAC 18 02-21-2012 09:35 AM
Pilot light going out often...and furnace making a big "boom" sound Beth777 HVAC 20 01-22-2011 05:27 PM
standing pilot in carrier furnace Ronnie1010 HVAC 3 01-12-2011 10:34 PM
Bryant Furnace pilot not lighting DGB HVAC 2 05-31-2009 12:47 PM
Urgent! House Cold, NO heat, pilot lit (Lennox) ThatGuy23 HVAC 15 02-05-2009 10:11 PM