-   -   carrier furnace (http://www.diychatroom.com/f17/carrier-furnace-168415/)
wpm paul 01-06-2013 06:02 PM
carrier furnace
my furnace will run until the room is to the thermostat set temp. It then goes to the blower only. The led flashes 1 short 1 long then 3 short, it is 8 years old
hvac dude 01-06-2013 06:36 PM
hi on the panel some place on the furnace there should be a label explaining the codes ,, look see what code it is and let us know which saftey its going off on,,model number to will help
Tator1076 01-06-2013 09:18 PM
It 13 code. Limit or roll out switch. Check filter
wpm paul 01-06-2013 09:46 PM
the filter is clean
hvac dude 01-06-2013 09:47 PM
did you check the codes on the panel ?? thats where you should start
wpm paul 01-06-2013 10:07 PM
model # 58msa
hvac dude 01-06-2013 10:09 PM
wpm please look on the panel for codes it will sure speed up the process ty
kirwinjd 01-06-2013 10:17 PM
Check the description of the codes on the panel. It will tell you what's going on.
I don't have the codes memorized.
how 01-06-2013 11:07 PM
I believe a code 13 means that a limit or roll out switch has be activated for more than 3 minutes.
Either the furnace has been overheating/ the flame has been rolling out the front of the heat exchanger/ the limit or rollout switch is faulty.
This is code that may be indicating a serious monoxide condition.
Do you have a/c? (dirty coil?) Are all the heating and return vents open or uncovered? Do you have dirty air filters in the heating outlets?
A electrical meter will tell you if either the main limit or the roll out switches have tripped.
A temp rise test will tell you if the furnace is actualy overheating.