Old 12-23-2009, 01:47 PM   #1
Carrier Cobra Gas Furnace Problem
We moved into a house this summer. The house was built in 1995. Not until this winter I notice the furnace that heats the house is not functioning properly. I was told the furnace is the original (installed when the house was built).
The furnace is a Cobra gas furnace by Carrier and is located in the attic. There are 2 thermostats, one upstairs & one downstairs.
The problem is the Flame-On duration varies between 3 and 7 minutes and is not long enough to warm up the house. For your information, I have recorded the sequence of the operation.
1. Surface Burner (Ignitor) On for 30 sec
2. Gas Valve Open & Flame ON for 50 sec
3. Blower ON for 3-7 minutes
4. Gas Valve Close & Flame OFF for 4 minutes (Flame shuts OFF even the temperature setting on the thermostat is not reached)
5. Blower OFF
6. Restart the cycle
Could the problem cause by the Flame Sensor?
The 2nd issue is the Blower-On-Time (4 minutes) after the Flame shuts OFF is too long. It blows cold air in the last 2 minutes period which makes house even colder. I adjusted "Blower Delay Time", but it didn't work.
Please help
carriercobra is offline   Reply With Quote
Old 12-23-2009, 02:13 PM   #2
MXer
3 legged dog's Avatar
could be a number of things. I'd start with verifying the tstat operation.
3 legged dog is offline   Reply With Quote
Old 12-23-2009, 02:32 PM   #3
Hi 3 legged dog,
Thank you for your assistance. Can you please be more specific about how to verify the state operation.
Old 12-23-2009, 02:44 PM   #4
MXer
You said there are two thermostats. How is this controling 1 heater?
Old 12-23-2009, 02:47 PM   #5
MXer
Originally Posted by carriercobra View Post
Hi 3 legged dog,
Sorry, I should have said thermostat.
Old 12-23-2009, 03:13 PM   #6
An old Tradesmen
Have you changed or cleaned your air filter recently.
Old 12-23-2009, 03:33 PM   #7
Hi beenthere,
The filter is new and is 3M Filtrete Ultra Allergen Air Filter. Could it be due to too much constrain of air flow?
Old 12-23-2009, 05:54 PM   #8
An old Tradesmen
Yes. Those are very restrictive air filters. And unless your duct was designed to use it. Don't use it.
Good chance either your furnaces high limit. Or your zone panels DATS are sensing too much heat and shutting down the burner to protect the furnace.
Old 12-23-2009, 06:35 PM   #9
hvaclover's Avatar
I figured he have one of those overpriced allergen type filters.
FYI for all DIYs: If you want allergy protection buy an electronic air cleaner or a media filter.
Those expensive filters that claim to to be good for allergies are just going to kill your furnace by causing it to over heat.
Just slow, not stupid.
hvaclover is offline   Reply With Quote
Old 12-24-2009, 09:54 AM   #10
HVAC Tech/ Browns Fan
Note You need to put the delay back on 4 min. becasue you need to get all the heat off the heat exchanger much as you can after burner shut off . It gaves it extra life time on exchanger.
Tator1076 is offline   Reply With Quote
Old 12-24-2009, 09:56 AM   #11
Plus if you have it turn off way to early. It will make the fan limit hot and short cycle the fan motor. That will save life on the run cap.
Old 12-29-2009, 07:30 PM   #12
Thank you all for the tips. It's the overpriced filter that causing poor performance. I replaced it with low MERV filter and the furnace is working properly.
Old 12-30-2009, 04:38 AM   #13
hvaclover's Avatar
What number was the MERV?
Old 12-30-2009, 12:47 PM   #14
It was MERV 12. The new one is MERV 7.
Problem with Rheem Criterion Furnace sweetsue777 HVAC 3 03-10-2012 12:13 PM
carrier 58mvp ingnitor part #/ignition problem GEAF HVAC 8 01-02-2011 05:00 PM
Carrier Weathermaker 8000, Gas Furnace Problem kiss44 HVAC 1 10-18-2009 09:27 AM
Carrier furnace problems BigK75 HVAC 1 07-30-2009 06:16 PM
Carrier Furnace Problem Boats1183 HVAC 1 11-11-2008 07:41 PM