Carrier 50jx942 Heater Wont Heat - HVAC - DIY Chatroom Home Improvement Forum
Old 02-28-2011, 06:51 PM   #1
carrier 50jx942 heater wont heat
my fan cycles on with the thermostat but the heater coil only gets 120v instead of 240v so it does not heat. had a power surge and brown out when problem started. think problem is at the heater sequencer and think it moght be the crr9-5 rectifier. anyone have any suggestions? mistake in tag line it is a carrier 50jx042 unit
martin1j is offline   Reply With Quote
Old 02-28-2011, 08:28 PM   #2
Where did you take the 110v. reading? Do the coils even warm up at all? Power surge....you sure you didn't bow a fuse link or maybe have a stuck sequencer or realy? You gettin' 220/240 to the heat kit itself?
Poppyloppy is offline   Reply With Quote
Old 02-28-2011, 08:49 PM   #3
110 was across heat unit. coils are fine and if sequencer and relay are by passed coils get 220 and heat up. i think the problem is either retifier crr9-5 that controls 24v to sequencer or sequencer itself. not sure how to check sequencer?
Old 03-02-2011, 06:43 PM   #4
Yea, both the relay and the seqencer are normally open and 24v closes them. If your getting 24v to them then they will show continuity after they close...either can have a delay (especially the sequencer) so you may have to wait a minute for the close
water heater heat traps BlueBSH Plumbing 6 10-22-2010 05:06 PM
Help with Heat Pump System Wiring AlanScott HVAC 11 10-10-2010 12:19 PM
carrier gas heater trieuphu99 HVAC 4 04-07-2010 12:03 AM
carrier 58ssb095ssc heat and air on together tiptopllc HVAC 3 10-20-2008 07:27 PM
Carrier Infinity T-stat and Performance heat pump gcole HVAC 3 10-03-2007 03:00 PM