Carrier 48SDN Control Board Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 02-05-2013, 12:46 PM   #1
Carrier 48SDN Control board problem
Hi,
I just replaced a dead controller board and the inducer motor won't start. I tracked it down to the Combustion relay (CR) on the control board which is in series with the inducer motor. This is a NO relay which should be closed by the processor when the stat calls for heat and then opened after the burner lights.
Suggestions, comments?
bausin is offline   Reply With Quote
Old 02-05-2013, 01:09 PM   #2
Roofmaster
Rewards Points: 2,210
Have you tried to put power directly to the inducer motor to see if it is functional? Check voltage first, but my carrier's inducer is 120 volts AC. Make sure the motor is good before you go any further.
Also, did you set up the board just like the old one, and is it an exact match?
Old 02-05-2013, 01:36 PM   #3
I have jumpered the relay; the motor turns and the furnace fires up.
The boards are almost exactly identical; the original is xxxx-116A and the new one is xxxx-117A. I could see no other difference. I hooked up all the wires, connectors and fuse from the old board.
There are no dip switches or other obvious configurable items. There is a jumper wire that says "Cut if CS used", but it is not cut on the original board.
Replacing Rim Board behind old Deck Ledger osubuckeye88 Building & Construction 11 10-26-2012 07:34 PM
New control board or fix it? Bobeht HVAC 26 01-18-2012 03:03 PM
Carrier 58 ga100-2 control board. Is it replaceable? Please help newman0112 HVAC 11 10-11-2011 07:39 PM
Carrier furnace not igniting-bad control board? stick_boy1106 HVAC 4 04-21-2011 06:28 PM
HELP!! NEW Control Board & Same Problem!! Steve72 HVAC 3 02-11-2009 02:48 PM