I have a natural gas furnace.
At first, I could not get the thermostat to turn the heat on.
I bought a new Honeywell digital thermostat.
I am 99% sure it's hooked up correctly as I replaced the 4 wires exactly as they were on the last thermostat.
Now I cannot get the furnace to shut off. The thermostat is programmed at 70 but the furnace keeps heating/blowing.
Ideas?
Is my circuit board screwed up?
Angus
My Albums
angus242 is offline   Reply With Quote
Old 03-04-2009, 05:27 PM   #2
GC/Master Plumber/Mech
Rewards Points: 560
Remove the stat from its base on the wall and see if the furnace goes off.
If it does then look at the stat and see if the fan is selected to the on position. If it is you may have the W and G terminal reversed.
If the selector is on auto then you may have a bad stat.
Old 03-04-2009, 05:34 PM   #3
angus242's Avatar
Fan in "ON" position, controls the fan properly.
In "AUTO" position, furnace always heats and blows regardless of programed temperature.
What are the chances that a brand new thermo is bad?
Is there another way to eliminate the thermo as the problem?
Angus
My Albums
Old 03-04-2009, 05:45 PM   #4
Rewards Points: 560
Did you remove the stat to see if the furnace stops?
Old 03-04-2009, 08:05 PM   #5
angus242's Avatar
When I disconnect the thermo and unhook the 4 wires, the furnace shuts off after a slight delay.
Angus
My Albums
Old 03-04-2009, 08:32 PM   #6
Rewards Points: 560
I would double check the wiring at the furnace control board to the stat.
White wire to W
Red wire to R
Green wire to G
Yellow wire to Y sometimes there isn't a yellow and blue is used
In other word just make sure that W is to W and R is to R and so on
R = Transformer voltage
W= Call for heat
Y = Call for cooling
G = Call for fan (blower)
Yes I have had stats right out of the box that were junk.
Also make sure the stat temp diff is set at 1 or 2 deg. Some stats have a .5 deg and that can cause some issues.
Old 03-04-2009, 08:53 PM   #7
angus242's Avatar
To me everything looks fine.
Does this mean I don't have to worry about the circuit board and I should try a new thermostat?
Angus
My Albums
Old 03-04-2009, 09:21 PM   #8
Rewards Points: 560
At the thermostat jump the R and W together.
This will cause the furnace to start..let it fire up and start blowing heat.
Then remove the jumper and the furnace should turn off after it cools down.
If this happens..then the control board is ok
Double check the stat set-up settings like;
Gas/electric/Heat pump
Temp differental
F/C
If you followed the set-up instruction and you are 100% right then yes get a different stat
Old 03-04-2009, 09:54 PM   #9
angus242's Avatar
OK, jumped and furnace did come on and blow hot. Removed jumper and it shut off.
Settings are correct; gas, heating cycle per manual and set to F.
I guess another thermostat is in order. As long as it wasn't the control panel on the furnace!
Thanks so much plumber!!!!!!!
Angus
My Albums
Old 03-04-2009, 09:58 PM   #10
Rewards Points: 560
Sounds good
Glad to be of help
What ever you buy for a stat..Please don't go with a Hunter
Braeburn, Honey Well, Robert Shaw and White Rogers are good brands
Good Luck
Old 03-05-2009, 08:55 PM   #11
angus242's Avatar
FYI, got a replacement Honeywell thermo and all's good!
Thanks again for the help!
Angus
My Albums
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 05:42 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 01:55 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 01:45 AM