Can I Use A 750 Millivolt Generator On A 250 - 500 Millvolt Gas Valve - HVAC - DIY Chatroom Home Improvement Forum
Old 10-10-2009, 05:27 PM   #1
Rewards Points: 89
Can I use a 750 millivolt generator on a 250 - 500 millivolt Gas Valve?
I am working on a really old wall heater with a B-60 gas valve. I know the generator is bad. The problem is the generator is not made anymore. The B-60 gas valve has instructions on which generator to use. It says...
USE WITH G.C. 250 MILLIVOLT (YELLOW BAND) PG-1 PILOT GENERATOR
it also says....
WHEN USED WITH T-70 HEAT ANTICIPATOR USE ONLY G.C. 500 M.V. BLUE BAND PG-9 GENERATOR.
So my question is, which replacement generator do I buy this is reasonable price? I know the PG-1 is not made anymore. I found a website that told me to replace it with a 750 millivolt generator. However, I don't want the extra millivolts to damage the gas valve. The replacement gas valve is really expensive.
stanlam is offline   Reply With Quote
Old 10-10-2009, 06:31 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,818
Is there a newer replacement wall heater available? At that age the valve may fail soon and is the heat exchanger safe? I always protect my behind first and won't retrofit anything even if there is the smallest chance of it not meeting some code or rating or design. Had a bad experience with a customer with lots of $$, and no brains try and sue me and my company. Do someone a favor and they stab you in the back.
Old 10-10-2009, 08:20 PM   #3
Rewards Points: 89
Gas Company said it's okay
The Gas Company I use actually have technician that come out and do free safety inspections and diagnosis. The technician said the heater is in perfect shape with the exception of the generator that needs to be replaced.
Therefore, thanks for your concern. Now I just need advise to know on which replacement generator to buy.
Old 10-11-2009, 10:30 AM   #4
To drop 750 mV to ~400 mV at some unknown, small, current level you need a series dropping resistor. It costs less than a dollar.
Since the elec. specs. on the internal resistance of generators and valves are a State Secret, you'd have to try different resistor values unless you measure the resistance of the gas valve coil and post back with the value.
E.g., if the coil reads 10 ohms and you want 500 mV across it the current in the coil must be 500/10 = 50 mA.
(750-500)mV/50 mA = 5 ohms
If the gas valve has an internal resistance of 3 ohms then you only need a 2 ohm resistor but let's start with 5.
The resistor will be dissipating 5 (0.05^2) = 13 mW. Choose a 1/8w or 1/4 w, 5.1 or 4.7 ohm resistor from (yuck) Radio Shack.
If you use no resistor the coil power will be twice normal and that will shorten the life of the coil, somewhat.
How old is that heater?
Old 10-11-2009, 11:03 AM   #5
Hvac Pro
yuri's Avatar
I think he needs a variable resistor as when the new generator starts to get weak the resistor needs to be variable or he will have no heat?
Old 10-11-2009, 11:22 AM   #6
A few fixed resistors, jumpered in as needed, are probably cheaper.
You have any measurements on what is considered "weak?" Open circuit output voltage goes down, internal resistance goes up, or both? How do these type of generators normally fail?
Old 10-11-2009, 12:07 PM   #7
Hvac Pro
yuri's Avatar
They get old and lose voltage. I don't dissect em just replace em. They are a series of thermocouples in a daisy chain. Read Fundamentals of Gas Utilization for more info.
Old 10-11-2009, 12:11 PM   #8
GC/Master Plumber/Mech
Rewards Points: 560
I would just put it in. Not a real big deal and I don't see it doing any damage.
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 10-11-2009, 01:29 PM   #9
If the control valve is designed for 250mv, then damage will occur if you hook up a 750mv TP. That would be like hooking 300 volts AC to an appliance designed for 110 volts AC.
Does the TP make any voltage? I have seen people replace the TP only to find that the problem was only a clogged pilot assembly.
log_doc_rob is offline   Reply With Quote
Old 10-11-2009, 01:35 PM   #10
Hvac Pro
yuri's Avatar
Those ITT General B60s had a small steel vent line from the side of the gas valve to the pilot burner. Very common that the end of it would get burnt off/plugged and not allow the valve to open. Now you got the old bean thinkin "old school".
Old 10-11-2009, 02:11 PM   #11
Rewards Points: 89
If you measure the wires directly from the generator, then it produces 150 milivolts. However, if you measure it through the thermostate, which is on the other side of the room, then it only produces 75 millivolts. I guess it loses millivots since the wire to the thermostate is either to long or to old.
Old 10-11-2009, 02:11 PM   #12
OK, book by Dutton.
OK, open circuit or closed circuit voltage decreases.
#26 AWG is ~4 ohms for 50' [100' loop distance] so I = 75mV/4 = 19 mA, assuming the wire and connections are good.
What's the voltage across the valve with this current? If it's 75 mV then the resistance of the valve should be 75/19 = 4 ohms. You may want to confirm this.
Old 10-12-2009, 05:33 AM   #13
I would try to disconnect the pilot line at the valve and blow the pilot assembly out with compressed air. Also, I deal mainly with gas fireplaces that use a 750mv TP and the manufacturers say that the stat should not have a wire run of more than 25 feet....that means the stat cannot be more that 12 1/2 feet away. Check the connections of your stat at the control valve and at the thermostat. I've seen a slightly loose connection cause voltage drops.
Old 10-12-2009, 06:11 AM   #14
Aman to that brother!
back in the day the majority of MV furnace calls were tarnished terminals.
Do twenty calls in a 12 hour shift just polishing the copper withe a SOS pad (steel wool fine grade). You might still be able to knock out 20 calls in this day and age if all you have are dirty flame sensor cleanings.
Really have to get your motor scooter running;
get out on the highway;
look for some adventure;
or what ever comes your way!
BORN TO RE-PAIR-AIR!!
WHERE'S THE BUSTED FURNACE?
hvaclover is offline   Reply With Quote
Old 10-12-2009, 10:44 AM   #15
Hvac Pro
yuri's Avatar
Cool dude. Was that you in your "Glory days". Bruce wrote a song about them, you can sing along to as well.
How to diagnose gas valve problems Nestor_Kelebay How To Guides 28 10-30-2013 04:19 PM
Double Check Valve installation (and a few other questions) secutanudu Plumbing 0 04-17-2009 07:42 AM
Need Replacement Gas Shut Off Value with Side Port for Pilot Light - Photos Available BobN HVAC 12 03-10-2009 12:02 AM
Toilet: water still coming from BOTTOM of Inlet Valve DIY Mom Plumbing 1 08-12-2008 12:43 PM
Best 1/2 inch water shut off valve. Nestor_Kelebay Plumbing 10 07-25-2008 11:16 AM