-   -   Can I use a 2-pronged run capacitor with this Bryant Air Condensor? (http://www.diychatroom.com/f17/can-i-use-2-pronged-run-capacitor-bryant-air-condensor-109009/)
dmmx3 06-27-2011 11:09 PM
I was told I could by a sales rep at Grainger, but after looking at wiring diagrams, and attempting instal, I am not sure.
The fan motor in my Bryant 127A (http://www.docs.hvacpartners.com/idc.../wd127a-01.pdf) went bad, so I bought this replacement (http://www.grainger.com/Grainger/GEN...JB5?Pid=search) with this capacitor (http://www.grainger.com/Grainger/DAY...&cm_vc=IDPBBZ2)
So, after putting the new motor in place, i wired as instructed, but was left with some wires leading no where. The fan now works, but I am getting no cold air.
Any help would be great. Thanks in advance.
JJboy 06-27-2011 11:29 PM
http://img691.imageshack.us/img691/1851/motor34.jpg
dmmx3 06-27-2011 11:39 PM
Thanks so much for the response and diagrams. This is what I did (i think). the motor has 4 wires.
one thing i possibly did incorrectly had to do with where i landed the white and black wires in the capacitor. those wires were bare on the end (no spades anchors - or whatever you called that), so i just stuck them through one of the holes in those squarish spade landings. One on the L1 side, and one on the L2 side.
also, one one of the wires i had to detach from the three pronged capacitor was a blue/pink wire that went into some plastic piece inside the unit. now that wire has no where to land? do i need it?
again, thanks very much.
JJboy 06-27-2011 11:45 PM
You need to connect Black and Write to L1 and L2 ( contactor )
Can you post picture?
dmmx3 06-28-2011 12:20 AM
1 Attachment(s)
sorta hard to see here, but the black wire on the left goes to the L2 side, and the purple wire on the right goes to the L1 side. These wires come from the fan motor.
they both go into those brass square with the small hole through the middle. Im not really even sure they are in the right place, but i couldnt see anywhere else to put them.
I am not getting cold air, so i must have done something wrong. Also, i forgot to mention earlier, but the fan seems to be on all the time. i turned the breaker on and reinstalled the disconnect, and the fan motor turned on on the outdoor unit, even tho the AC was turned to OFF on the t-stat.
dmmx3 06-28-2011 12:26 AM
2 Attachment(s)
Here are two other photos i took:
1 is the old capacitor. there were three wires going in, including the yellow one which went to the contactor and the blue/pink one which went to some plastic thing inside the unit that was attached to copper pipe (some sort of pressure control?). These wires now land no where on the end that was on the capacitor.
The other photo shows the new capacitor with the two wires coming out of it. not sure if this helps...
thanks again for your help.
danny12122 06-28-2011 01:47 AM
uh oh
So using the capacitor u got for the fan was fine but u still need the old cap in there for the compressor. Try moving the purple and black wires to the opposite side of the contactor ( T1 and T2). This will solve the constant running problem. Now take the old capacitor and find somewhere to mount it in the panel. I like to use duct strap and self tapping screws to do this but if u don't have those don't worry it can just hang there for now but be sure to use electrical tape to cover the terminals on top after u have wired it in. Also be sure that it does not touch any other wire terminals inside that panel. Now take the yellow wire and connect it to the old capacitor exactly how it was ( connect from contactor to terminal on capacitor marked com) now take the blue wire and hook it up how it was (connect toterminal marked herm on capacitor). That's it, oh and if I understood right u said u just shoved the fan wires through the little holes on the brass thingy, well when u move them to the other side of the contactor use spade connectors. Hope all goes well good luck.
beenthere 06-28-2011 04:50 AM
You removed a dual run capacitor. It also ran your compressor. Look at its rating if you still have it, and go an get another like it with the exception that the smaller value must match what your fan motor needs. And then wire it back in like it was.
dmmx3 06-28-2011 08:10 AM
i connected the two wires to T1/T2 instead of L1/L2, but then when i turned on the power the fan did not turn at all. I can hear a "click" as the t-stat is moved from off to cool, but no fan. so, i put them back to L1/L2.
i connected yellow and blue to old capacitor as instructed. i'll upload a diagram of what i have in a minute. However, it appears i am still getting no cold air.
dmmx3 06-28-2011 08:27 AM
1 Attachment(s)
Here is a diagram of what i have currently. symptoms are:
1) the outdoor fan runs constantly - as soon as power is brought to the unit
2) i am not getting cold air. (note that i was getting cold air before i replaced the fan motor)
clocert 06-28-2011 08:41 AM
As mentioned, you need a dual capacitor(3 prong). you don't get cold air is because your compressor is not running.
dmmx3 06-28-2011 09:07 AM
I have connected the 3 prong as well, so shouldn't that work?
Also, is it possible the 3 prong dual capacitor is bad? could that have caused the original issue (fan motor getting power as it was hot to the touch but was not running.) ?
im going to go pick up a new dual run capacitor to replace both the old and new capacitor anyway.. i will know soon enough i suppose.
dmmx3 06-28-2011 01:48 PM
i picked up a new dual capacitor (3 prongs). i tried two things:
1) using only the 3 prong capacitor, i connected blue wire to herm, yellow to C, and brown to Fan. I capped the brown/white wire coming from the fan.
This resulted in the fan motor not working
i then tried:
2) using both the new 3 prong capacitor and the new 2 prong, i connected the blue and yellow into the new 3prong, and the brown and brown/white into the 2 prong. this resulted in the fan working, but no cold air.
im really at a loss here. any ideas? thanks so much.. it's hot!
JJboy 06-28-2011 01:57 PM
you need to check the C from compressor
dmmx3 06-28-2011 02:08 PM
what do you mean?