Old 03-23-2010, 11:43 AM   #1
Can I split airflow from a 640cfm hood, 10" round to two 3.25x14 ducts
Hi. We are trying to upgrade our range hood as part of a kitchen remodel. Our current system vents via one 3.25x14 rectangular duct, down through the wall behind the range, then transitions to a 6" round under the house.
My range wall is a standard 4" depth, studs on 16", so 3.25x14 seems to be the largest rectangular duct the wall can facilitate.
The new hood is more powerful - 640cfm - requiring a minimum 8" round or equivalent. According to this website (http://www.engineeringtoolbox.com/eq...ter-d_205.html) the equivalent rectangular duct would need to be larger than 3.25x14; larger than my interior space between the studs and drywall.
So my question is, can I run TWO 3.25x14 rectangular ducts parallel to eachother in the wall (stud separating them) to meet minimum airflow? I realize I would have to join them at the top somehow, and not sure how to calculate the resistance of splitting the airflow like that. (The new hood has a 10" round vertical exhaust port at top, so I must make a 180 degree transition from that, to the two 3.25x14 rectangular ducts). Once under the house, the two rectangulars would rejoin/transition to a single 8-10" round to run out of the house.
Any tips are much appreciated. Jay
ductdawgz is offline   Reply With Quote
Old 03-23-2010, 01:51 PM   #2
If you have "standard" dimensional lumber, then the cross sectional area of a single stud space should be equal to an 8" round duct.
An 8" round duct has a cross sectional area of about 50.25 sq.in. (4*4*PI).
2x4 dimensional lumber is actualy 3.5"x1.5". So on 16" centers, you've got 14.5" or a total area of 3.5 x 14.5 = 50.75 sq.in.
Since you can build metal ducts to any dimensions, if you don't have to have the duct insulated, you should be able to build a metal duct the full 3.5 x 14.5 size.
Or is there something else I'm missing?
HooKooDooKu is offline   Reply With Quote
Old 03-23-2010, 05:52 PM   #3
An old Tradesmen
You mean besides a 3¼ X 14½ is barely able to move as much air as a 7" round/oval duct.
Old 03-23-2010, 07:31 PM   #4
if you hve to transition at the stove eliminate the stud, install header if bearing wall and have 30.5x3.5
The older I get the better I was
Old 03-23-2010, 07:32 PM   #5
I wouldn't argue with your wall spacing, but HooKoo, your equivalent airflow specs seem to conflict with specs from the calculator results obtained here:
That calcs the 3.5x14.5 to only 7.35 round capacity at best.
Old 03-24-2010, 12:24 AM   #6
One of the things I wanted to point out was that you were using measurements of 3.25 and 14.25... I couldn't understand why?
Of course, like I said, my numbers were based only on cross sectional area... the page you're referencing takes into account the flow difference between a round duct and a rectangular duct.
Now I don't know if there are any code conserns in spliting the vent into two vents, but if a single stub cavity is equal to a better than a 7" round duct, any losses associated with splitting the flow is more than compensated by using the equivilent of TWO 7" round vents to vent a single 8" round vent.
Old 03-24-2010, 05:54 AM   #7
An old Tradesmen
OP.
How much air do you WANT it to remove/vent.
Start with that. And then see what size duct you need to use. Look at your hoods CFM rating at different static pressures(And no, the FR on a ductulator is NOT static pressure).
Then figure out where the make up air will come from that the exhaust hood needs.
For 50CFM of 10° colder air your make up air brings in. You add 540BTUs per hour of run time.
EG: 70°F indoor temp, 40°F outdoor temp.
500CFM of make up air 30°F cooler then indoor temp=16,200BTUs of heat to warm it up to room temp(1 hour of hood exhaust run time).
Old 03-24-2010, 09:26 AM   #8
Learning by Doing
Leah Frances's Avatar
Beenthere makes a good point. I can always tell if I forgot to turn off my exhaust fan because you can feel the breeze in my drafty house several rooms away.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 03-25-2010, 01:47 PM   #9
An old Tradesmen
Just think what would happen if your house was tight.
Old 03-25-2010, 03:35 PM   #10
Learning by Doing
What would happen?
- pull exhaust from furnace into the house?
Old 03-25-2010, 04:16 PM   #11
An old Tradesmen
From the furnace and or water heater.
On a standard gas water heater it can also pull the burners flame out of the combustion chamber and burn up the water heaters insulation. And cause a fire. Possible on some older furnaces also.
Could also over power bath fan, and draw fumes from it.