A/C Charging Question - HVAC - DIY Chatroom Home Improvement Forum
Old 05-18-2013, 07:56 PM   #1
A/C charging question
Hi,
I just wanted to check my a/c unit to make sure there is the proper amount of refrigerant. What methods can I use to check that?
markharmon is offline   Reply With Quote
Old 05-18-2013, 08:05 PM   #2
Rewards Points: 13,300
Pick up phone, call HVAC company.
Old 05-18-2013, 08:38 PM   #3
Rewards Points: 582
Originally Posted by markharmon View Post
Hi,
hooking up a set of gauges see whats going on...ben sr
Old 05-18-2013, 09:15 PM   #4
Rewards Points: 1,192
If you aren't certified,the homeowner metheod would be to use a thermometer to check air temperature at registers. Look for temps between 50 and 55.
bobelectric is offline   Reply With Quote
The Following 2 Users Say Thank You to bobelectric For This Useful Post:
ben's plumbing (05-19-2013), HVAC1000 (05-20-2013)
Old 05-18-2013, 09:17 PM   #5
Hi Ben,
How do I know what pressure my system should be at after hooking up hi and low side gauges?
Old 05-18-2013, 09:22 PM   #6
Rewards Points: 79
You can't check charge based on pressures alone. You need indoor wet bulb temps, super heat and sub cool, and required super heat and sub cool requirements. Also, you need to be EPA 608 certified to connect gauges to residential AC systems.
Ebierley is offline   Reply With Quote
Old 05-18-2013, 09:35 PM   #7
Be a whole lot easier for you to post the data than for us to go through all the steps and formulas.
Outside air temp
Indoor return wet bulb and dry bulb temps
Supply wet bulb and dry bulb temps
measured cfm
suction line temp
liquid line temp
make and model of AC
type of metering,txv or fixed orifice
Old 05-18-2013, 10:06 PM   #8
An old Tradesmen
Rewards Points: 6,590
Super heat and sub cooling are used to determine if the unit is charged correctly and operating properly.
The Following User Says Thank You to beenthere For This Useful Post:
Old 05-18-2013, 10:58 PM   #9
Right so why are the other members asking for wet bulb temp, dry bulb temp, return air temp, etc.? How do I find out what pressure my system should be operating at?
Old 05-19-2013, 05:37 AM   #10
An old Tradesmen
Indoor wetbulb(best taken at the indoor coil) is used to determine what the super heat should be.
There is no "the system should be at this pressure" answer.
At 86 degrees outdoor temp and an indoor wetbulb temp of 63 degrees, a fixed metering device system has a target super heat of 11 degrees.
At 86 degrees outdoor temp and an indoor wetbulb temp of 67 degrees, a fixed metering device system has a target super heat of 17 degrees.
At 86 degrees outdoor temp and an indoor wetbulb temp of 71 degrees, a fixed metering device system has a target super heat of 23 degrees.
The saturation pressure/temp of the suction must of course be above 32F, so the evap coil doesn't freeze.
Old 05-19-2013, 07:30 AM   #11
Rewards Points: 582
then check super heat and sub cool to see if you have the proper charge on system based on reading.....ben sr
Old 05-19-2013, 07:34 AM   #12
Rewards Points: 582
all these steps are relative to checking a/c systems.....some techs go a different way to arrive at a point where this system is either properly charged or under charged..ben sr
Old 05-19-2013, 09:24 AM   #13
If I get a set of gauges how do I know what the system pressure should be at?
Old 05-19-2013, 09:43 AM   #14
Rewards Points: 79
What everyone is trying to tell you, there is not a pressure it should be. The correct pressure depends on all the readings we are telling you. Depending on load on the system the pressure changes constantly. What is the correct pressure today is the incorrect one tomorrow. A real tech does not check charge by pressure alone. With the cost of gauges, EPA card, thermometers etc. it would be cheaper to find a good tech.
Why are you concerned with the charge? Did it not perform well last year? The charge will be the same unless the system has a leak.
Old 05-19-2013, 09:58 AM   #15
Rewards Points: 1,216
The very first thing to know is what type of refrigerant is in the equipment. The next thing to know is what pressures they operate at. The next thing is to buy a set of gages compatible with the type of refrigerant your using. You should also have a set of superheat thermometers, a digital temperature analyzer with 2 leads to check 2 temperatures at the same time. Then you will need a jug of refrigerant the type that's in the unit. Next you might need a scale to weigh in th refrigerant. Now after all that you really shouldn't be putting gages on a unit to check the freon unless you really have done many checks before that. The reason, every time someone puts gages on a unit it losses a couple Oz's of freon which has to be calculated back in to the unit.
Probably should call a pro. Call me now or call me later it'll cost you more later when you F--- everything up.
No Warranty Means- If it breaks in half you get to keep both halves.
COLDIRON is offline   Reply With Quote
The Following 2 Users Say Thank You to COLDIRON For This Useful Post:
ben's plumbing (05-19-2013), Ebierley (05-19-2013)
Charging battery while using it vs charging till empty will this affect battery life? jratftcc Electrical 2 04-01-2013 11:41 PM
Another Aluminum Siding prep question aribert Painting 6 03-14-2013 02:48 PM
EV charging loads and time switches - rating question flasherz Electrical 4 03-11-2013 02:35 AM
Plumbing for new shower kit question noviceshock Plumbing 6 03-02-2013 09:11 PM
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 09:19 AM