Bypassing The Control Board For Temporary Heat - HVAC - DIY Chatroom Home Improvement Forum
Like Tree8Likes
  • 1 Post By Mrbuilder
  • 2 Post By Mrbuilder
  • 2 Post By supers05
  • 1 Post By beenthere
  • 2 Post By beenthere
Old 11-22-2016, 04:24 PM   #1
" I Can Fix It "
Mrbuilder's Avatar
Rewards Points: 134
Lightbulb
bypassing the control board for temporary heat
Been running down problems with my package unit. Goodman 4 ton roof mounted. Had a dead short. Found and fixed. Installed new inducer and limit sw. Now, have no voltage to gas valve. Have a pro coming tomorrow, but need heat tonight. Jumped off red stat wire and valve opens. Can I jump off white stat wire for heat tonight. Shouldn't the valve only open when heat is called for ? Just want to bypass board till I get a new one tomorrow. Any help is appreciated guys n gals Thanks
P.S. unit is PGB048125-1A Manufacture date 2003 if it helps
Getting cooler and waiting on the rain !!! lol
Mrbuilder is offline   Reply With Quote
Old 11-22-2016, 04:39 PM   #2
Rewards Points: 3,674
Re: bypassing the control board for temporary heat
If the ignition control is separate from the board then maybe. If the ignition/burner control is part of the main board then no this is very unsafe and should not be done. You'll be dumping raw fuel into the heat exchanger during prepurge.
roughneck is online now   Reply With Quote
Old 11-22-2016, 04:44 PM   #3
Rewards Points: 1,284
Thus lies one of the many reasons houses go BOOM.
Improperly "fixed" gas heaters.
If you do this make sure that you take some stay awake pills, so you can monitor this all night long and be there to shut it down if a lot of gas is dumped out before it fires up.
ED
de-nagorg is online now   Reply With Quote
Old 11-22-2016, 04:49 PM   #4
" I Can Fix It "
Mrbuilder's Avatar
Rewards Points: 134
OK, Thx roughneck. have another heat source, just wanted to save a little time. I have a radiant heater. Just didn't want to get out the pipe dope and those pesky adjustable wrenches. lol Hmmmm however roughneck, it is on the roof and I could get out the other end of the house before it collapsed. Don't know if the wife can move that fast....hmmmmm.
appreciate it
MTN REMODEL LLC likes this.
Old 11-22-2016, 04:54 PM   #5
" I Can Fix It "
Mrbuilder's Avatar
Rewards Points: 134
Hey de-nagorg at least I asked ............... lol
Besides, I've put it in print and " and in the cloud " insurance won't pay now.......lol
MTN REMODEL LLC and de-nagorg like this.
Old 11-22-2016, 11:21 PM   #6
Rewards Points: 46
Quick answer.... No!
Looked up the wiring diagram for that unit. It's a integrated board, half the safety is built into it. I'm not even sure how you got it to light off? (manually?)
They are easy to fix. They guy should be in and out quickly, if he has the board with him.
Cheers!
supers05 is offline   Reply With Quote
Old 11-23-2016, 06:26 AM   #7
An old Tradesmen
Rewards Points: 6,592
A small description of what would happen.
The gas valve would open at the same time the inducer/combustion blower starts. raw/unburnt gas would be flowing into the heat exchanger while the board goes through its pressure switch safety timing, allowing the entire heat exchanger to fill with gas, and gas to come out the vent/exhaust. The pressure switch timing would then prove the inducer/combustion blower is working, and the HSI would be energized. Sometime after the HSI's temp rose above 1,120F, the gas would ignite. The RTU would blow apart, the gas line would break becoming a flame thrower. A large hole would be in what is left of the roof. And a fire would be burning in the house. Anyone under that section of the roof, would probably be killed. Might also get a couple of the neighbors homes also.
supers05 likes this.
Old 11-23-2016, 07:21 AM   #8
Rewards Points: 46
Would be great for a movie scene. Very action packed...
People might actually take us seriously after seeing that.
Cheers!
Old 11-23-2016, 09:45 AM   #9
" I Can Fix It "
Mrbuilder's Avatar
Rewards Points: 134
Lightbulb
FYI guys, the unit is on a curb directly above kitchen table. Maybe have the son in law having lunch, and slip to breaker box in basement and turn on breaker................hmmmmmm
Old 11-23-2016, 04:24 PM   #10
An old Tradesmen
They thought these were good ideas.
de-nagorg and supers05 like this.
15A Fuse On Control Board! justplumducky HVAC 18 10-20-2015 10:08 PM
VisionPRO Setup Functions & Heat Pump infoskr HVAC 43 07-12-2015 05:28 PM
Ducane Furnace Control Board Questions dmason83 HVAC 4 11-15-2012 08:15 AM
Driveway gate control board lightening issues walt1122 Electrical 6 11-05-2012 11:51 AM
Changing Control Board Questions -- HSI module and AC wire connection humdinger0102 HVAC 7 11-17-2011 01:16 AM