Burned wire on ac capacitor common


Ok. Getting warm this season and decided to check the ac to make sure it works. The past couple years I have had the ac not work upon first startup. The first year was a leak in the coil. It just popped when I turned it on and everything leaked out. The second year the unit turned on but no cold air. I replaced the capacitor to no avail. Called a tech and he pressure tested the entire coil, which was fine, and found a small leak in the valve where someone had tried to plug it years before it looked. He replaced the valve and that portion of the pipe. Everything worked perfect for the whole season. This year I turned it on and no cold air. Opened the side and saw the burned connection on the common. Replaced the wire and bought another new capacitor. Now the unit still does not blow cold air but it the fan runs but I cannot tell if the compressor is running or not. The pipe does not get cold at all. Maybe I re-wired it back wrong?
The compressor is a copeland.
Thank you in advance.

http://i.imgur.com/7pcGt.jpg

http://i.imgur.com/uUIWG.jpg

Advertisement

Elkypro is offline   Reply With Quote
Old 03-16-2012, 02:17 PM   #2
Part of the Clover Leaf
 
Join Date: May 2011
Location: NW Burbs of Detroit Mi.
Posts: 1,107
Rewards Points: 500
Default

Burned wire on ac capacitor common


If the comp is running then you may have a no refrigerant in the system.

Did you say you can feel air coming out the ducts?

Advertisement

hvac5646 is offline   Reply With Quote
Old 03-16-2012, 03:48 PM   #3
Newbie
 
Join Date: Dec 2011
Location: Chicago area
Posts: 28
Rewards Points: 25
Default

Burned wire on ac capacitor common


Yes, there is the normal amount of air coming out of the ducts.

What would be a good way to see if the comp is running? Take off the fan unit and turn it on?

Last edited by Elkypro; 03-16-2012 at 04:17 PM.
Elkypro is offline   Reply With Quote
Old 03-16-2012, 09:04 PM   #4
thermal-medics.com
 
Join Date: Feb 2012
Location: Phoenix, AZ
Posts: 48
Rewards Points: 25
Default

Burned wire on ac capacitor common


you can hear the compressor running when the outdoor fan motor kicks on. if its a copeland scroll then you should hear the hi pitch at start up. you can find out quickly if you take an insulated screwdriver and push that plunger on the front of the contactor - holding the insulated handle. then you should hear both come on.

just make sure you discharge that capacitor if you are going to touch any wires after testing it - they pack a punch.. i know this.
thermal-medics is offline   Reply With Quote
Old 03-17-2012, 02:17 AM   #5
Newbie
 
Join Date: Mar 2012
Posts: 6
Rewards Points: 10
Default

Burned wire on ac capacitor common


Quote:
Originally Posted by thermal-medics View Post
you can hear the compressor running when the outdoor fan motor kicks on. if its a copeland scroll then you should hear the hi pitch at start up. you can find out quickly if you take an insulated screwdriver and push that plunger on the front of the contactor - holding the insulated handle. then you should hear both come on.

just make sure you discharge that capacitor if you are going to touch any wires after testing it - they pack a punch.. i know this.
it could be that your compressor is bad you could ohm out the windings take the plug off the compressor and ohm out start, run, terminals that will let youo know if it is actuall compressor if you run low on charge you will experience freezing of a/c
heatingman is offline   Reply With Quote
Old 03-17-2012, 12:12 PM   #6
Newbie
 
Join Date: Dec 2011
Location: Chicago area
Posts: 28
Rewards Points: 25
Default

Burned wire on ac capacitor common


Thanks for the tip of the contactor. I pushed in the plunger for a few seconds and the compressor came on just fine. So time to call the hvac to find another pesky leak
Elkypro is offline   Reply With Quote
Old 03-17-2012, 12:35 PM   #7
An old Tradesmen
 
Join Date: Oct 2008
Location: PA
Posts: 26,418
Rewards Points: 4,486
Default

Burned wire on ac capacitor common


I don't see that you have a pressure switch that could keep the contactor from pulling in.

You may not have 24 volts going to the outdoor unit.
beenthere is online now   Reply With Quote
Old 03-17-2012, 03:28 PM   #8
Newbie
 
Join Date: Dec 2011
Location: Chicago area
Posts: 28
Rewards Points: 25
Default

Burned wire on ac capacitor common


Quote:
Originally Posted by beenthere View Post
I don't see that you have a pressure switch that could keep the contactor from pulling in.

You may not have 24 volts going to the outdoor unit.
I'm sorry, I am very much a laymen when it comes to electrical work. Would you mind explaining if that is good/bad as well as what the difference that would make?
Thank you
Elkypro is offline   Reply With Quote
Old 03-17-2012, 03:52 PM   #9
An old Tradesmen
 
Join Date: Oct 2008
Location: PA
Posts: 26,418
Rewards Points: 4,486
Default

Burned wire on ac capacitor common


Could just be the the contactor is bad. or that you don't have 24 volts to the contactor from the thermostat.
beenthere is online now   Reply With Quote
Old 03-18-2012, 01:15 AM   #10
thermal-medics.com
 
Join Date: Feb 2012
Location: Phoenix, AZ
Posts: 48
Rewards Points: 25
Default

Burned wire on ac capacitor common


You are probably right on the loss of refrigerant. All you started with was as visual inspection of the run cap and found a burned terminal. You replaced and confirmed the outdoor fan motor and compressor came on.

1. if you leave the unit off for an hour or so the pressures will stabilize and you should not have a low/high pressure cut out.

2. If you have the whole shebang working in unison compressor, outdoor fan, indoor blower and you can feel the refrigerant pipes and they are lukewarm - both of them- than I would be sticking to your gut instint instead of just swapping parts if you are not into working with a voltmeter.

I would leave it off until you can verify the refrigerant is still there and not keep running it or the repair prices will add a 0 on to the final tab in a hurry.
thermal-medics is offline   Reply With Quote
The Following User Says Thank You to thermal-medics For This Useful Post:
Coliver0630 (03-18-2014)
Old 03-18-2012, 10:01 AM   #11
Newbie
 
Join Date: Dec 2011
Location: Chicago area
Posts: 28
Rewards Points: 25
Default

Burned wire on ac capacitor common


Thanks for the responses guys. Much appreciated!

Advertisement

Elkypro is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Proper Use of Green Wire Nuts HooKooDooKu Electrical 16 06-29-2012 07:41 PM
ceiling fan wicked97 Electrical 4 08-21-2011 09:12 AM
convert 3 wire range junction box to receptacle filby Electrical 0 06-05-2011 02:33 AM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 04:30 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM




Top of Page | View New Posts