BTU Calculations - HVAC - DIY Chatroom Home Improvement Forum
Old 03-28-2012, 08:31 PM   #1
AGWhitehouse's Avatar
BTU Calculations
Anyone have a good site and/or formula for BTU calculation loads?
I'm researching ventilation air heating requirements and am trying to find out:
640cfm @ delta T 15 deg. F rise (100% humidity) = ?BTUs?
640cfm @ delta T 15 deg. F rise (50% humidity) = ?BTU?
It's for intake air from a geothermal source (55 dwg. F +/-) being brought to room temp (70 dwg. F +/-) with the varying humidity loads. I'm not looking for exact stuff, just theoretical schematic planning stuff...Thanks!
Life's too short...so enjoy it!
AGWhitehouse is offline   Reply With Quote
Old 03-29-2012, 05:23 AM   #2
An old Tradesmen
Rewards Points: 6,548
(TR*1.08)*CFM=BTU
15*1.08=16.2
16.2*640=10,368 BTUs of heat.
The humidity won't matter, 100%RH compared to 50%RH has less then a 20 BTU an hour difference.
The Following User Says Thank You to beenthere For This Useful Post:
AGWhitehouse (03-29-2012)
Not good at calculations Thurman Electrical 3 12-30-2010 09:30 AM
heat pump heat lost calculations ??? mark2007 HVAC 1 05-25-2010 09:09 AM
Box-Fill Calculations MartinD Electrical 10 01-26-2010 07:58 PM
Screwed up calculations, How bad is this? diyintexas Building & Construction 1 09-30-2009 10:30 AM