Bryant 340MAV - Control Board Just Flashes - HVAC - DIY Chatroom Home Improvement Forum
Old 12-05-2010, 01:36 AM   #1
Bryant 340MAV - Control board just flashes
I have a Bryant 340MAV furnace with a United Technologies HK42FZ009 control board. When the thermostat calls for heat, the blower comes on, but the burner doesn't and there is no heat. The inducer motor never comes on. The LED on the unit flashes steadily, but the AC polarity is correct. The unit does not respond to a request to self-test. Jumping the test terminal to common just results in a relay clicking. There is no error code read out and the unit doesn't sequence through the component test.
Any ideas what's wrong? Any other test I should run?
billd17 is offline   Reply With Quote
Old 12-05-2010, 08:30 AM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,856
Probably a bad circuit board. Relays eventually stick and fail.
Old 05-14-2011, 06:58 PM   #3
Billd17,
A couple days ago i noticed that my furnace does not work. I have the same control board like yours HK42FZ009. When the thermostat calls for heat, the blower comes on, but the burner doesn't and there is no heat. The inducer motor never comes on. The LED on the unit flashes steadily. The unit does not respond to a request to self-test. Jumping the test terminal to common just results in a relay clicking. There is no error code read out and the unit doesn't sequence through the component test.
Have you diagnozed what was the problem with your Bryant 340 MAW. It seems that my furnace has the same problem.
Has anyone have any opinion what may be the problem. Control board or someting else.
kingk is offline   Reply With Quote
Old 05-14-2011, 07:24 PM   #4
I'm Your Huckleberry
Rewards Points: 2,270
Bad board, relay or tripped high limit switch. When a high temperature (excessive heat) limit switch trips the blower will come on as it is trying to push any heat out of it. The burners are cut off until that limit switch is reset or replaced as there is no point in producing more heat if there was excessive heat to begin with. That is how a furnace is wired, to not produce more heat and to try and blow out any heat that may be in there IF a high temp limit switch has tripped any time that furnace is turned on.
High limit switches trip because of restrictied air flow such as a blocked return air (filters) and/or a dirty and blocked evaporator coil.
Now if the high limit switch has tripped then more than likely there will be a flash code for this problem.
Doc Holliday is offline   Reply With Quote
The Following User Says Thank You to Doc Holliday For This Useful Post:
kingk (05-15-2011)
Old 01-02-2016, 02:31 PM   #5
Rewards Points: 2
Originally Posted by kingk View Post
Billd17,
Did the Blower motor turn off after 90 seconds? If not the a limit may be open.However the board should still pick up the error. Check continuity of the limits and rollouts in addition to replacing the board.
tbynum is offline   Reply With Quote
Old 01-02-2016, 02:55 PM   #6
Rewards Points: 3,770
This thread is 6 years old.......hope the guy still isn't trying to troubleshoot it.
roughneck is online now   Reply With Quote
The Following User Says Thank You to roughneck For This Useful Post:
Bitters (01-02-2016)
Tags
340mav , bryant , hk42fz009
Whirlpool refrig. problem ken1415 Appliances 147 02-25-2017 12:27 PM
Heil NUG5075BFB1 A/C -One Control Board? zeloma HVAC 0 06-14-2010 12:42 PM
York gas heater control board replacement spyvan HVAC 5 12-29-2008 07:12 AM
Installing deck ledger board over foam board? RickT Building & Construction 5 11-06-2006 10:50 PM
Ruud a/c control board replacement ? kourso HVAC 1 07-20-2006 09:33 PM