Old 10-19-2010, 10:32 PM   #1
Bryant 3 wire pilot won't hold
I have a Bryant 376BAW036075 that the burners won't ignite. It is a 1989 vintage furnace. This is what is happening.
1. thermostat calls for heat
2. inducer motor comes on
3. ignitor starts to spark
4. pilot ignites and burns and then it extinguishes
5. ignitor sparks
6. pilot ignites and burns and then extinguishes
7. Main burner valve never opens
This sequence continues indefinetly. I have replaced the three wire pilot and the gas valve and also the inducer motor control board. Nothing I do changes the above sequence.
janibre1 is offline   Reply With Quote
Old 10-19-2010, 10:41 PM   #2
HVAC / Plumbing
sounds like it's not proving pilot flame. If it doesn't prove pilot. It won't open main valve & pilot will go out
kenmac is offline   Reply With Quote
Old 10-19-2010, 10:47 PM   #3
The pilot is proving, but the pilot won't hold and it extinguishes when the main burner valve is suppose to open. If it was just a matter of the pilot not proving why would the pilot go out if the call for heat was never broken?
Old 10-19-2010, 10:51 PM   #4
HVAC / Plumbing
That's why the pilot goes out. Some of the older furnaces proved the pilot was lit by the ignitor/ spark rod. Do you have a seprate sensing rod ?
Old 10-19-2010, 10:53 PM   #5
No, there is not a seperate sensing rod.
Old 10-19-2010, 10:56 PM   #6
HVAC / Plumbing
Ok, then it senses through the ignitor rod & it isn't proving pilot flame shutting down pilot gas. then, it will re-try, still doesn't sense pilot flame & shtus pilot gas off again. It will do this over & over
Old 10-19-2010, 11:02 PM   #7
I thought that it sensed the flame through a warp switch that is built into the pilot assembly. The only wire that goes to the electrode looks like a spark plug wire and it connects to the ignitor module.
Old 10-19-2010, 11:07 PM   #8
HVAC / Plumbing
It does have a bi metal switch in the pilot . When it gets hot enough it makes up and applies 24v to the gv. but if it goes out b-4 it gets hot enough to make the connection it won't open the gv. It senses flame back through the plug wire. The sensor wire or the board is bad. You might try to clean the sensor or the wire where it connects to the board
Old 10-19-2010, 11:13 PM   #9
I see I didn't mention it before but a also tried to replace the ignitor board and it didn't help. I suppose that the electrode wire might be defective even though it passes a spark throught it. I can try a new one tomorrow.
Old 10-20-2010, 07:56 AM   #10
HVAC / Plumbing
All you have to do is replace ignitor rod & wire & you have a new furnace.
at 21 yrs old . I would have replaced the furnace
Old 10-20-2010, 01:37 PM   #11
Poor people have poor ways. The customer say's they can't afford a new furnace otherwise it would have been a gonner.
Old 10-20-2010, 01:43 PM   #12
HVAC / Plumbing
they have already spent alot of $ in parts alone. I would check the heat exchanger real close for cracks/ holes
Tags
bryant, three wire pilot
Older Carrier Pilot Burner Problem cliffkot HVAC 23 04-29-2011 06:58 PM
HVAC three wire motor to six wire motor Leo Caproni HVAC 5 10-18-2010 02:23 PM
Carrier/Bryant/Payne 3 wire gas pilot assy 1991 furnace GBG HVAC 14 09-24-2010 07:10 PM
20A Breaker, 14 gauge wire? joside Electrical 12 08-25-2010 10:41 AM
Resource for understanding gas valve? darsunt HVAC 19 02-04-2009 12:08 AM