Boiler Won't Fire Back Up - HVAC - DIY Chatroom Home Improvement Forum
Old 02-04-2013, 09:00 AM   #1
Rewards Points: 16
Question
Boiler won't fire back up
I have a Weil-Mclain boiler and I recently replaced two radiators. After I turned the system back on it fired up fine, but then I noticed I had a bad solder joint near the new rads. I powered down the system and drained it to fix the leaky joint. When I turned the system back on the pilot lit, the circulator ran, water was moving through the pipes, but the boiler just would not fire.
I tied the thermostat wires together thinking the thermostat might be the issue, but no change. I also swapped out the transformer on the system, but again nothing.
Any ideas?
This_old_dump is offline   Reply With Quote
Old 02-04-2013, 10:53 AM   #2
MarginallyQualified
Rewards Points: 2,464
Originally Posted by This_old_dump View Post
...the pilot lit ... but the boiler (main burner) just would not fire.
Any ideas?
Start with the thermocouple to be sure it's producing enough power.
It's probably fine but is inexpensive and often the culprit.
Similarly... touch and tighten all the wiring connections.
The next step up is the combination valve itself.
The same control voltage running the thermostat and pump relay should be feeding the valve too... either there's a fault in that circuit telling the valve to open or the valve itself is bad.
Old 02-04-2013, 01:47 PM   #3
Rewards Points: 1,300
Is this an electronic ignition or a standing pilot system?
danpik is offline   Reply With Quote
Old 02-04-2013, 02:25 PM   #4
Rewards Points: 16
It is a standing pilot system
Old 02-04-2013, 04:05 PM   #5
If it is a standing pilot then it should have a thermocouple like this...
If the pilot is staying lit then it is good. Check the wiring going to the gas valve to see if you are getting 24 volts there with the thermostat calling for heat. Check between the TH and the TR terminals with a meter.
Tags
radiator problems , weil mclain
Slantfin Galaxy Boiler Pressure Mystery chiefswabjockey HVAC 18 11-15-2011 05:37 PM
Electrical Fire seansy59 Electrical 1 10-24-2011 05:57 PM
Burnham boiler series 2 clicking sound on fire up mookie118 HVAC 1 12-31-2010 12:16 PM
Burnham boiler banging/thumping noises quadradeuce HVAC 6 10-02-2010 09:55 PM
Oversized boiler solution (radiant heat)? gbwillner HVAC 5 02-14-2010 06:28 PM