Does this flame look right? Burnham Seires 2 NG boiler. The blue portion looks to be "attached" to the burner rather than above the burner.
If you don't stand behind our troops, please feel free to stand in front of them.
Joe F is offline   Reply With Quote
Old 01-26-2014, 11:51 AM   #2
Rewards Points: 242
flame suppose to be blue with yellow tip. 2nd picture looks a little weak.
only way to tell is to check gas pressure from the gas valve using a monometer.
hvac instructor is offline   Reply With Quote
Old 01-26-2014, 02:55 PM   #3
Not the only only. Clock the boiler's input using the gas meter.
hvac benny is offline   Reply With Quote
Old 01-26-2014, 03:35 PM   #4
Joe F's Avatar
Rewards Points: 294
OK, so I assume with all other gas appliances off, I watch the meter while the boiler runs. That will give me cfm. What do I do with that number?
Old 01-26-2014, 03:59 PM   #5
how
Rewards Points: 1,070
All other gas appliances off.
The unit you are wanting to test..... running for a couple of minutes.
3600
x the calorific value of the gas in your local area (1050 here)
x the size of the dial on your meter that you are measuring (.25 /.5 / 1 )
divided by the seconds it took that dial to rotate once.
Compare that with the BTU's on the rating plate of your boiler.
There is another adjusting figure to multiply if your meter is metric.
how is offline   Reply With Quote
Old 01-26-2014, 04:21 PM   #6
Joe F's Avatar
Rewards Points: 294
How do I determine the caloric value? My gas is 1.048 therms per CCF.
Old 01-26-2014, 04:51 PM   #7
That will be 1048btuh/cf.
Old 01-26-2014, 05:05 PM   #8
Joe F's Avatar
Rewards Points: 294
So if I'm following the concept correctly, I'm going to compare what the unit is using to the input rating (198,000 btu/hr) and see if it's low or high. That will tell me if I need to get someone out to adjust the gas valve, correct?
Old 01-26-2014, 05:54 PM   #9
An old Tradesmen
Rewards Points: 6,098
Thats 1048 BTUs per CF.
New Boiler for an Office - Got Two Quotes, but What Do We Need? Prolow Plumbing 0 09-17-2012 07:10 AM
I Need a New Boiler. What do i need to know New Boiler Co Plumbing 0 10-23-2010 07:03 PM
boiler producing no flame and no hot water merrygoround Plumbing 0 08-08-2010 12:01 PM
radiant boiler flame laenbro HVAC 10 10-15-2009 01:22 PM
Utica Boiler Pilot light on but will not flame up! MGB150HID HVAC 2 12-10-2007 05:48 PM