I didn't power off EAU at breaker when replacing Honeywell T8085D thermostat with Lux 1500 (possibly shorting the blue to the red wires). Now, I couldn't get the fan, A/C nor the heating started. I have a Comfortmaker furnace using a White Rodgers Main Control Board 50E47-130.
My questions are:
1. Power at the breaker is good, but couldn't measure power from the wirings. Is this confirmation that the transformer is fried?
2. Transformers are on the ones on the White Rodgers control board, correct?
3. What terminals to measure from the control board to verify the transformer is gone?
4. Do I need to replace with the exact same White Rodgers control board? Or, can I replace with another control board model (that is newer, better, cheaper?)
Thanks in advance.
samvee is offline   Reply With Quote
Old 01-20-2010, 07:55 PM   #2
1) what "wirings" are you checking.
2) most transformers are not built into the circuit board.
Check for a low voltage fuse or breaker first. Check the continuity across the line voltage side of the transformer to see if it's good.
Old 01-21-2010, 07:34 PM   #3
1) I measured across R & C wires (red and blue in this case) and there was no voltage reading.
2) The transformer below measures 22V across.
The controller board is as follow:
http://www.white-rodgers.com/wrdhom/...pg0278_281.pdf
When measuring across TH & TR of the control module, it does not have any voltage reading. L1 and TH measures about 125Vac.
Please advise where to go from here. Thanks.
Old 01-21-2010, 07:46 PM   #4
Is that transformer in the furnace? Can't tell from the picture but it looks like a for a doorbell. Can you post a picture of the lower half of the furnace please.
Old 01-23-2010, 05:45 PM   #5
zoom out pictures of furnace are below:
Old 01-23-2010, 06:39 PM   #6
Transformer should be in that metal box in front of the blower.
Old 01-24-2010, 03:20 AM   #7
I measured 24V across the transformer on the right side (with the cover switch pressed), but C and R terminal still has no voltage. With the transformer working, how come there's no reading across C and R?
What is the black box on the left side?
Where should I go from here?
Old 01-25-2010, 05:09 AM   #8
The secondary voltage measured zero from the transformer, so that is why I am not picking up power across R & C. I measured the wrong wire from the transformer the night before...
Will stop by local hardware store to get a replacement transformer to try.
In regards to air filter for the furnace, what is the best kind? I heard that electrostatic filter will stress the system too much. Any truth to that?
Thank you MARTY for your help!!
Old 01-25-2010, 07:20 AM   #9
I like a simple pleated filter. None of that ultra allergen junk though.
transformer questions Steelhead Electrical 8 10-25-2009 09:39 PM
How to install Aprilaire transformer? Studly HVAC 9 09-18-2009 10:44 AM
Comfortmaker RPJ - Bad Transformer? olgranddad HVAC 2 12-26-2008 12:10 PM
Central Ac transformer question Rschrei518 HVAC 4 10-20-2008 09:21 PM
Different color wires on new doorbell transformer.... ConstantChange Electrical 31 11-22-2007 12:08 AM