Trying to get the specs of the blower motor in my furnace to see if it is capable of keeping up with the new heat pump and coil I had installed.
It is a Trane TUE080A936K0
Thanks in advance for any help!
Snipeston is offline   Reply With Quote
Old 07-22-2012, 08:48 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
that has a 3 ton blower in it.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 07-22-2012, 08:50 PM   #3
I am sorry, I should have been more specific...I need to know the CFM rating...
Old 07-22-2012, 08:53 PM   #4
AKA HVACTECHFW
1200 cfm based on 400 cfm per ton necessary for air conditioning, what size of HP do you have?
IT IS WHAT IT IS
Old 07-22-2012, 08:54 PM   #5
New unit is a York 3 ton unit with just under a 4 ton coil (046)
Replaced a Trane 3 ton unit and coil
Old 07-23-2012, 04:55 AM   #6
HVAC Contractor
Rewards Points: 336
If it worked okay with the Trane 3 ton, it should work okay with the York 3 ton. Coil size doesn't really have much to do with CFM, assuming the coil is properly installed and serviced of course.
The rated CFM of that furnace ranges between 717 and 1393, depending on motor speed and static pressure. At a .5 static on high speed, the fan performance charts says you'll deliver 1296 CFM. Note this is the TUE1B080 series, but the fan performanc data should be the same.
scottmcd9999 is offline   Reply With Quote
Bryant Plus 90 - No Blower Ducaticorse HVAC 13 01-03-2015 04:39 PM
Odd Fireplace Outlet Behavior permagrin Electrical 2 12-17-2011 08:06 AM
Heat comes on but blower never does aczer HVAC 12 02-13-2011 06:57 AM
Blower shuts off even when set to 'on' fetzer85 HVAC 1 07-05-2010 11:48 AM
Carrier 58MXA Wiring Blower Switch 63012753 HVAC 0 10-06-2009 09:09 PM