Blower Motor Cycles On And Off Very Often Only In A/C Mode - HVAC - DIY Chatroom Home Improvement Forum
Old 06-22-2009, 09:07 AM   #1
blower motor cycles on and off very often only in A/C mode
The blower motor cycles on and off very often, but only in cooling mode.
In cooling mode only (when thermostat is set for cooling and set temp is lower than room temp). The outside condensor will run continuely, but the blower motor (fan) will cycle on and off every often (on a few min and off a few min), this is happening regardless of the fan setting of on or auto.
At first I thought there is some kind of thermo cutoff in the blower due to over heating, but if I turn off ac or set the temp above room temp in cooling mode and switch fan to on mode from auto mode, the blower will run fine for several hours straight without any problem.
Thanks in advance for any help.
carrara is offline   Reply With Quote
Old 06-26-2009, 07:16 PM   #2
Picture of the controler
Here is a picture of the white rodgers controler, please help if you can.
<img src="http://i221.photobucket.com/albums/d...a/41f50927.jpg">
blower motor cycles on and off very often only in A/C mode-dscn1637.jpg
Old 06-26-2009, 09:04 PM   #3
as seen on tv
Rewards Points: 150
Is the t-stat at desired setpoint when indoor blower shuts down?
qbert is offline   Reply With Quote
Old 06-26-2009, 09:31 PM   #4
JohnH1's Avatar
It could be eather the WR board or the blower mtr cooling speed. When you put the fan switch to on and run only the fan it is operating the motor in the heat speed setting.
Try and switch the heating and cooling speed wires on the WR board and run it in the fan on setting again this will run the cooling speed. If it then runs without fault it must be the board.
JohnH1 is offline   Reply With Quote
Old 06-26-2009, 10:43 PM   #5
No. the indoor blower will run for a few min and off a few min until the desired temp is reached while the outdoor unit is running non stop. (during very hot temp outside, the indoor may never reach the set temp)
Old 06-26-2009, 10:47 PM   #6
Can you tell me which two wires to switch to test the board? I am kind of guessing the ones on the right side of the board? Just want to be sure? What about the dip switch? where can I find a wiring diagram? (I was not able to find anything on white rodgers site) Thanks a lot.
Old 06-27-2009, 02:21 PM   #7
You may have a contactor that is putting an excessive draw on the low voltage which is causing the blower relay to drop out from a lack of voltage. Could also be a voltage drop from the thermostat.
If you have a meter check your board, r to c, y to c and g to c with the ac running. Then turn ac off and turn the fan on and check all again. Let us know what you find.
SKIP4661 is offline   Reply With Quote
Old 06-27-2009, 08:48 PM   #8
HVAC / Plumbing
I would say to check the cooling speed terminal at the board & see if you are loosing voltage (110-120) when the fan stops.. If not I would say something is getting hot on the board & dropping the voltage to the relay that feeds the fan
kenmac is offline   Reply With Quote
Old 06-28-2009, 09:51 PM   #9
JohnH1's Avatar
Look at were the wires are plugged in at on the right side of the board the terminals are usually marked heat and cool. they are probly the black for cool and the blue for heat.