I am replacing an old noisy bathroom exhaust fan that currently has a 4" roof jack/cap and 4" ductwork. According to the proper calculations, I would need a new exhaust fan rated at 190 CFM. However, I can't find any 4" exhaust fans with CFM ratings this high. The roof is 7/12 pitch and I have no intention of climbing on it to change out the 4" roof jack with a 6" version - or hiring it done.
The duct work requires 3 turns and is 17' long. My goal is to replace the old fan with one that will do the best job possible using the 4" roof jack and that is less than 2 sones.
I just read on Nutone's website that you can use larger duct work than the duct outlet of an exhaust fan - it will actually improve performance by reducing static pressure.
My question is: (1) Should I buy the largest 4" CFM exhaust fan I can find and convert it at the fan outlet to 6" and then back to 4" at the roof jack. Or, (2) Should I buy a 6" exhaust fan rated at 190 CFM and convert it to 4" at the roof jack? Would this meet code? Which would work better - move more air and remain quiter?
Lyndon is offline   Reply With Quote
Old 02-05-2012, 08:28 PM   #2
GC/Master Plumber/Mech
Rewards Points: 560
Internation residential code states for bathrooms that the exhaust fan needs to be 50 cfm for intermittent and 20 cfm for a continuous fan.
I'm courious how you came up with the cfm you need?
4 " duct is only rated about 80 cfm
6 " duct is rated about 110 cfm
Requardless of what you do if you restrict it to the 4" roof cap (Approx 80 cfm) then you are only wasting money unless you run it all in 6" to include the termination cap.
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
The Following User Says Thank You to Plumber101 For This Useful Post:
ben's plumbing (02-05-2012)
Old 02-05-2012, 08:34 PM   #3
Rewards Points: 13,458
Your also loosing a lot of CFM's with the long run and all those turns. Not a great lay out.
Old 02-05-2012, 08:39 PM   #4
http://www.panasonic.com/business/bu...s-_-msn-_-1348
May find what you looking for here.
Old 02-06-2012, 07:15 AM   #5
Per Panasonic's website:
17' solid ductwork
45' = 3 elbows/turns
30' = 4" Roof cap
For a total of 92' Equivalent Duct Length (EDL)
Room is 11' 4" x 11' 7" x 9' ceilings = 1182 cubic feet
Using Panasonic's scale I would need an exhaust fan rated at 190 CFM.
Calculations using other means: 1190 cubic feet / 7.5 = 160 CFM
or 1190 x .13 = 160 CFM
or 1190 / 60 minutes per hour x 8 ACH = 160 CFM
However, these other calculations does not take into effect the bends in the duct work or the length.
So if 6" duct is rated at 110 CFM, how would you ever install an exhaust fan that would exhaust more than 110 CFMs? I've seen 6" exhaust fans rated MUCH higher than 110 CFMs.
Old 02-06-2012, 07:16 AM   #6
I am well aware of this fact but the facts ARE the facts!
Old 02-06-2012, 07:35 AM   #7
Disabled wood vet
titanoman's Avatar
Rewards Points: 1,004
I had no idea a fart fan was such a technical apparatus.
titanoman is offline   Reply With Quote
Tags
bathroom ceiling fan , bathroom fan exhaust , bathroom fan venting , duct sizing , ducting calculation
Using Bathroom Exhaust During Demo DetroitEE Building & Construction 10 01-17-2011 02:32 PM
Dryer exhaust duct not connected inside dryer frankrizzo Appliances 4 02-09-2010 08:47 PM
Splitting duct to a new bathroom nalishaw HVAC 4 10-31-2009 01:22 PM
Exhaust fan / duct question vit HVAC 4 10-19-2009 03:51 PM
Duct sizing C44 HVAC 3 03-23-2009 04:24 PM