I have an Armstrong Heat Pump HVAC unit with electrical strips for auxilliary heat. When my thermostat engages the heat pump in the heat setting, (I also have an emergency heat setting but this is not what is on.), my heat pump comes on along with the fan but the heat strips come on as well. When the desired temp is reached on the thermostat the heat pump goes off but the heat strips and fan remain on. You can set the thermostat to off but this does nothing the only way to shut the strips and fan off is to turn off the breaker in electrical panel. Any ideas would be greatly appreciated.
kevinm2512 is offline   Reply With Quote
Old 02-27-2013, 07:44 PM   #2
An old Tradesmen
Rewards Points: 6,846
Heat sequencer stuck closed. Needs to be replaced. Or a short in the wiring.
Old 02-28-2013, 08:55 PM   #3
I replaced the sequencer and get the same results
Old 02-28-2013, 08:58 PM   #4
An old Tradesmen
Trace out wires, look for a short.
Old 02-28-2013, 09:01 PM   #5
Any chance it could be the fan control board.
Old 03-01-2013, 04:10 AM   #6
An old Tradesmen
Possible. But you should use a meter to check if the board is getting a heat call on the W terminal or not, before just changing out the board.
Old 03-01-2013, 04:10 AM   #7
An old Tradesmen
heat pump freezing problem av-geek HVAC 8 02-02-2012 07:16 PM
Trane XR11 heat pump problem with compressor not always starting right away.. mikebdub HVAC 11 01-29-2011 05:38 AM
Governments Renewable Heat Incentive SMurray Green Home Improvement 1 10-24-2010 08:30 AM
Urgent! House Cold, NO heat, pilot lit (Lennox) ThatGuy23 HVAC 15 02-05-2009 09:11 PM
HUGE Icicle problem & Heat Loss zaibas Roofing/Siding 5 02-01-2009 03:33 PM