-   -   American Standard intermittent inducer problem with presssure switch warning (http://www.diychatroom.com/f17/american-standard-intermittent-inducer-problem-presssure-switch-warning-127720/)
no such user 12-26-2011 04:13 PM
We have an American Standard high efficiency gas condenser furnace with electronic ignition model # CUC100A948A5 and an electric air filter, installed in 2003. (We bought the house last year.)
We've been investigating this problem for a week now, by ourselves, with my partner's mechanically-inclined father, and with a furnace tech. None of us can recreate the problem on command, and no one is sure what it is.
After starting up and running normally for several hours (usually around 8 hours or more), when the thermostat calls for heat, the inducer motor will start to run then stop repeatedly, struggling to get started. As this happens, the pressure switch clicks, the gas valve clicks, and sometimes the unit will glow and then the burners ignite and it runs normally until the next cycle, sometimes it just glows and nothing ignites, sometimes the inducer just keeps trying to get started the unit shuts itself down. If we leave it off for awhile, it runs fine until the whole problem repeats. While it's faulting, the indicator light blinks three times, which is the code for a pressure switch issue.
We tested the voltage of the pressure switch and fan--everything appears normal. The pressure tubes are intact and connected. Blowing on them shows that the switch is working. The condenser drainage tubes appear to be draining properly. The PVC exhaust is venting with enough pressure that it doesn't seem like it's blocked. The intake and exhaust lines are level, so water isn't building up in them, and the fan makes no water-swishing noises at any point.
The tech replaced the board, but that didn't fix it. He came back and put the old board back in (and didn't charge us for it). He also tested the voltage near the burners and flame sensor and a bunch of other places--everything seemed to be correct. Then he noticed the ground was disconnected or loose--not sure whether we or he may have knocked it loose--but it's connected now and the unit is still doing the same thing.
We replaced the pressure switch before the tech came back, but it's doing the same thing, still with the 3 blink code when it faults.
Last year the blower had to be replaced. The tech said it was due to the filter not being cleaned for so long. We regularly slean the filter and have had no problems until now, including when running AC sometimes in the summer.
Here are some of my theories, after reading as much as I can:
1. Is it an issue with the limit switch? Could the switch be getting stuck on the high limit after the unit heats up and preventing the unit from starting as a safety? (But wouldn't that make the indicator flash for a limit switch problem?)
2. Could the heat HSI need replaced?
3. Could the flame sensor be the problem?
4. Is it the inducer fan, even though it appears to be getting the right voltage?
5. We've shut the unit off to work on it a bunch of times, but haven't shut the circuit breaker on and off for that part of the house. Does that matter? There was a power surge in our neighborhood the other day, but the problem had started before that.
I really appreciate any help anyone can offer!
how 12-26-2011 04:50 PM
Not much stops an inducer from operating during a call for heat except for a faulty thermostat or thermostat wires, a faulty board, momentary power interuptions, bad connections from the board to the inducer, faulty inducer motor or capaciter (if it's got one).
With the problem being so intermitant (8 hours) it's difficult!
You could try throwing on a cheap thermostat replacement.
Ohm test the seperated r & w thermostat lines while checking and moving them around to see if there are any minute line disconnections. Checking for any other loose grounds from the board to the house service which can make boards behave erratically.
But the most telling info would come from setting up a V meter thats t'ed to the inducer power line and the next time the inducer starts going on & off, turn on the meter to see if the power is steady or not.
hvactech126 12-26-2011 04:51 PM
You need to check the venting. Ensure that it is clear (no obstructions). Can you also post a furnace model number instead of the control number? You need to verify if the inducer is getting power the entire time it is starting and stopping, you also need to verify voltage from W to C on the control board while this is happening.
ben's plumbing 12-26-2011 05:32 PM
had this same problem with another unit just like it.. we were thinking it was a bad board....almost changed it....turned out to be bad thermostat....may be worth changing stat out 1st...
harleyrider 12-26-2011 06:14 PM
assuming that this unit has sealed combustion, remove the burner door, and let the unit run........does it still act up or does removing the burner door seem to fix the issue?
Doc Holliday 12-26-2011 06:20 PM
It could be #4, draft inducer motor. Check ameprage draw when you first turn the system on and it's running normally and then check amperage draw of the inducer when it's struggling to start.
It will if you notice the amps dropping completely to zero tha you need to determine if you are receiving steady voltage to it during that time.
If you are receiveing a steady voltage to the inducer yet the amps are all over the place, either dropping or ramping up or spiking, then change the inducer.