Old 10-13-2008, 07:04 PM   #1
Newbie
 
Join Date: Oct 2008
Posts: 1
Rewards Points: 10
Default

American Standard Freedom 80


When I first turned the furnace on this fall, no heat only cold air. Fan motor runs and the vent motor starts up and then stops right away. Glow plug does not come on. LED flashes 9 times, board says chek igniter, but I took igniter to neighbors house, plugged it in his furnace and it works.

Filters are clean, gas is on, vent fan motor stops right after starting. The unit is 8 years old.

Is my ciruit board bad?? I have power to the circuit board for the vent fan and the igniter.

If anyone can help with answers, I would appreciate it.

Kenneth L

Kenneth L is offline   Reply With Quote
Old 10-13-2008, 09:10 PM   #2
Electrician
 
SD515's Avatar
 
Join Date: Aug 2008
Location: Near Jackson Michigan Area
Posts: 1,451
Rewards Points: 502
Default

American Standard Freedom 80


There's a few things to check. Use a multi-meter to check for 120V going to the igniter. Check the fuse on the board...should be a 3 amp blade type (protects the 24V system circuits). Check that the transformer is putting out 24V.

__________________
Kyle

Just because you can, doesn't always mean you should
SD515 is offline   Reply With Quote
Old 10-16-2008, 10:00 PM   #3
Newbie
 
Join Date: Oct 2008
Posts: 6
Rewards Points: 10
Default

American Standard Freedom 80


Kenneth L,
Funny this issue should arrive. Today as a matter of fact I ran into the same issue. I was getting a ignition fault code of 9 blinks. I investigated the ignitor only to find odly enough a loose wire. As far as ohming out the ignitor it should be any where from 15 to 20 ohms. I received 14.7 which is just fine. I put the ignitor wires back together only to find the unit would fire up just fine. this sparked my interest. no pun intended. So I wiggled the ignitor connection to find small arks happening at this terminal. This was a down draft unit. also the unit would throw a high limit open signal. 4 blinks. all this stems from a loose ignitor wire. wiggle them in and out at the white hazey terminal. if the terminal moves more than 1/4 inch or so replace with the new upgraded version. Good luck.
bryguy is offline   Reply With Quote
Old 10-17-2008, 12:28 AM   #4
Member
 
hvaclover's Avatar
 
Join Date: Oct 2008
Location: Suburbs of Detroit Mi
Posts: 3,704
Rewards Points: 2,000
Default

American Standard Freedom 80


What everybody should take away from Bryguy's post is that the fault codes are only a guide, not a diagnostic conclusion.
__________________
Just slow, not stupid.
hvaclover is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
American Standard Freedom 90 Question bobjbc HVAC 21 01-03-2013 07:08 PM
3 - flash code, american standard freedom 90 furnace dfferg HVAC 25 03-05-2012 12:21 AM
American Standard freedom 90 tokio_mx3@yahoo.com HVAC 2 06-01-2008 10:19 PM
American Standard Freedom 90 help. JEVSkeeter HVAC 1 03-25-2008 10:26 PM
American Standard freedom 90 3 flash code t_cel HVAC 1 12-23-2007 06:38 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.