Amana Code 3 Pressure Switch - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 12-22-2008, 07:58 PM   #16
Hvac Pro
yuri's Avatar
Rewards Points: 1,102
That is VERY Dangerous!! That pressure switch proves that there is proper draft thru the heat exchanger/proper air for combustion! You can have a fuel rich mixture and an explosion. Better to get some temporary space heaters and get a pro to fix it properly. The ventor fan may be a dud/not getting up to speed etc. Unit needs to be checked by a pro with a manometer.
Old 12-22-2008, 08:08 PM   #17
he was here and said it was the pressure switch and someone will be back in the morning so it should be checked then.
Rich3791 is offline   Reply With Quote
Old 12-22-2008, 08:31 PM   #18
I will use the space heaters that they left, I do understand your concern.
Old 12-22-2008, 08:42 PM   #19
That furnace appears to be to a new Amana/ Goodman furnace. I have dealt with a few drain issues with these units. The drains have to be configured by the installer according to the position it is installed (horizontal or upflow). Have seen them configured wrong. The manual should show the proper configuration. Also have seen venting issues. Not enough slope back to the furnace. The inducer would hold the condensate in the vent pipe until the call for heat was over. Then the condensate would rush back to the furnace and flooded the inducer. Inducer would not close the pressure switch for the next cycle because of being flooded. Had to install a drain T in the horizontal exhaust run to catch the condensate.
SKIP4661 is offline   Reply With Quote
Old 12-22-2008, 08:58 PM   #20
Hvac Pro
yuri's Avatar
I hope his installer understands all that. Good Points.
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 06:42 PM
Pressure switch stuck open? 2 areas im looking @ 1001miles HVAC 42 12-03-2012 04:51 AM
New Pressure Switch -- low water pressure chach Plumbing 4 01-18-2009 10:50 PM
Bad pressure switch? gshock HVAC 3 11-13-2007 08:15 PM
PAYNE Pressure switch error code 23 WRKPA HVAC 1 02-04-2006 07:37 AM