I stood there while the Reliance tech diagnosed my furnace and it honsetly seems like there is no suction from the fan to activate these switches although when he applied light suction to them they seemed to operate properly. He then said it was the switch and ordered replacements which were dropped off and I can't wait for 4 days for them to come back so I installed it and it still doesn't work. What could the probem be? an improper seal on the fan? The vent isn't plugged outside.
Rich3791 is offline   Reply With Quote
Old 12-22-2008, 02:29 PM   #2
Are you sure you got the right switch? Can you applying suction to the switches/vacuum hose and complete the ignition phase? Have you pulled the inducer fan to see if its dirty or you have dirty, junk, or pest squatters? Have you back-probed the switches to be sure you are getting continuity?
dac122 is offline   Reply With Quote
Old 12-22-2008, 02:48 PM   #3
Does this furnace use two plastic pipes for venting or metal pipe. If it is plastic check the intake pipe where it attaches to the furnace for leaves and such.
SKIP4661 is offline   Reply With Quote
Old 12-22-2008, 02:51 PM   #4
If I apply suction the furnace will start up. It's brand new and was installed last Thursday hasn't worked properly since the initial start-up. He didn't pull the inducer fan but did probe the switches. There doesn't seem to be flow from the inducer fan hose hook up even when he disconnected the exhaust pipe to check for blockage in the exhaust pipe.
Old 12-22-2008, 02:52 PM   #5
plastic and it's new so no leaves etc to be found and yeah I checked to see if it was kids messing around too.
Old 12-22-2008, 02:54 PM   #6
Is this furnace a new install?
Old 12-22-2008, 02:55 PM   #7
If its high efficiency maybe the condensate drains are plugged or kinked.
Old 12-22-2008, 03:05 PM   #8
Yes it's a new install and no the drains don't look plugged at all but I will check when I get home.
Old 12-22-2008, 03:09 PM   #9
Did the installer follow the manufacturers specs for running your intake and exhaust pipes: certain size pipe, lengths, number of elbows, etc.? Either that you have some kind of infancy failure or defect in the draft inducer.
Old 12-22-2008, 05:49 PM   #10
An old Tradesmen
Rewards Points: 7,376
On some brands, you have to fill the trap for them to work.
What brand and what is the model number of the furnace.
Old 12-22-2008, 06:07 PM   #11
Seems to be working when I remove this yellow plug is that correct?
Old 12-22-2008, 06:35 PM   #12
Hvac Pro
yuri's Avatar
Rewards Points: 2,286
If you can carefully remove the cover from the burner box try starting it with that cover off. If it works then Buddy has a blocked intake problem. My installers once squirted a bit too much silicone on a fitting for a Armstrong and it plugged the intake screen. B4 that go outside a put your ear to the intake pipe and see if it sounds like it is sucking air when it tries to start or blow cigarette smoke at it. You should be able to feel a draft going into that pipe.
Old 12-22-2008, 06:45 PM   #13
yep it was sucking and exhausting now it's working with that yellow plug removed.
Old 12-22-2008, 06:51 PM   #14
Hvac Pro
yuri's Avatar
That may be dangerous!! You are relieving some pressure and that is a NO NO. The switches need to be properly checked with a manometer. Sounds like a venting problem to me. Try the other test I gave you.
Old 12-22-2008, 06:55 PM   #15
When I took the yellow plug off there was some water in the and it seems to work and no water coming out now. I've been bypassing the pressure switch for two days now letting it run a cycle and no CO on my CO detector.
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 05:42 PM
Pressure switch stuck open? 2 areas im looking @ 1001miles HVAC 42 12-03-2012 03:51 AM
New Pressure Switch -- low water pressure chach Plumbing 4 01-18-2009 09:50 PM
Bad pressure switch? gshock HVAC 3 11-13-2007 07:15 PM
PAYNE Pressure switch error code 23 WRKPA HVAC 1 02-04-2006 06:37 AM