AC outside unit will not come on
My inside unit comes on but outside does not. The unit is only two years old. I replaced a capacitor that looked kind of bad, but still did not run. The board inside the unit(Rheem) is displaying a number 5.
Thomas124 is offline   Reply With Quote
Old 03-01-2012, 09:47 PM   #2
Rewards Points: 6,652
Check the disconnect outside to see if it is still giving voltage to the unit. If the disconnect is one that you remove the link and it is missing, or the breakers are off, then you have found your problem.
Old 03-01-2012, 10:12 PM   #3
All breakers are on.....there is voltage at the disconnect.
Old 03-01-2012, 10:17 PM   #4
Missouri Bound's Avatar
No fan, no compressor? Control relay working, loose connection on low voltage?
Do you want it your way or the right way?
Old 03-01-2012, 10:25 PM   #5
REP
On a call for whichever,do you have 24 volts at the contactor?Is there 220 volts on one side of the contactor?
REP is offline   Reply With Quote
Old 03-01-2012, 10:32 PM   #6
What are you using to measure the voltage, and what voltage are you getting?
Old 03-01-2012, 11:30 PM   #7
somewhere on your condenser probably on the inside of the access cover you removed to replace the capacitor it will tell you what a #5 or s fault code is. one thing to chech are the pressure sensors if the fan quit it would trip the high pressure switch inside the condenser. some of them have alittle red button on top of them that can be reset. does the contactor pull in when you set your t-stat to cool. If it does you have 24v out there if it doesn,t check for 24v if it is present yor contactor is bad.
rsarg is offline   Reply With Quote
Old 03-01-2012, 11:34 PM   #8
Thomas...does the fan run now?....or does nothing run? A limit switch certainly could be the problem.
Old 03-02-2012, 08:03 AM   #9
Willing to listen
Rewards Points: 219
Code 5 on that control board = compressor will not run. Eventually that will transition to L5 (lockout) after the control tries for 6 hours to restart the unit and see a normal run. That unit does not have a traditional contactor, it is built onto the board.
Those units ship with factory installed hard start components. Per Rheem you should check:
1. Run Cap
2. Start Cap
3. Voltage level at the board and compressor
4. Broken wires, loose connections, miswiring
5. Check compressor motor windings for continuity
6. Check for open compressor internal protector
7. Check for excessive liquid refrigerant in the compressor
You may simply need to reset the lockout now that you have changed the one cap. You can do this by cycling line voltage or low voltage...or the TEST button on the control board...but be advised that 1 second after pressing TEST the control will attemp to energize the compressor, and be aware that there are locations on that control and unit with 240VAC live. Also be aware that the control board has a 3 minute short cycle delay anytime you cycle power or remove a call, so you have to wait for that to expire or use the TEST button to bypass if you are expecting to see the unit start running immediately.
BTW...I am assuming this is a JEZ series unit with a single digit 7-segment LED on the control board. The codes are slightly different on a JEC communicating unit that has a 2-digit LED...so clarify the type please.
Done That is offline   Reply With Quote
Old 03-02-2012, 10:13 AM   #10
Thanks for the help so far, I need to check some of the things mentioned when I get home.
LED with displaying the # 5 list these:
1.Check for damaged, miswired or wrong run capcitor
2.Check for damaged or miswired start capacitor and relay
3.Check voltage levels at ICC and compressor
4.Check for broken wires, loose connectors, or miswired
5.Check compressor motor windings for continuity
6.Check for open compressor internal protector
7.Check for excessive liquid refrigerant in compressor
Some things I have check, mainly the obvious ones loose, damaged wires. Everything looks fine. The unit is only two years old and has never been worked on before. I have a volt meter and need to check some of the things above, but might need a little guidance along the way of doing that.
Old 03-02-2012, 10:34 AM   #11
Willing to listen
Rewards Points: 219
I know this is a DIY site but on a 2 year old unit is there any reason you would not have the installing contractor come out an take a look? Those units carry a pretty good warranty I believe, and if you accidently damage that control board or something else it's going to be a bit pricey.
Old 03-02-2012, 06:17 PM   #12
Yes I hear you on the ac contractor should come out and check it out. I was trying to save a little, the parts would be covered under warranty but not labor. So $80.00 to just come out and then whatever labor to fix the problem. When I started to check it out myself and the trouble pointed to the capacitor that cost me $10 to replace I was hoping to get lucky. So I was still hoping it could be a easy fix or a part that I could replace for less than the minimum the contractor will start at $160.00
Old 03-03-2012, 07:13 AM   #13
Rewards Points: 1,216
When you get home turn your thermostat all the way down with the cool on go out side and check the voltage across the two small wires.
If you have 24 volts the problem is in the unit out side if you don't have 24 volts you have a problem inside.
The inside components are not sending the voltage outside to the unit.
COLDIRON is offline   Reply With Quote
Ruud Pack unit "KABOOMS" upon First Light Up of the Day! Wirenut2tite HVAC 18 12-15-2012 11:11 AM
Had an Aire-Flo AC installed, looking for opinions mikemcd HVAC 14 08-01-2011 05:07 AM
Old carrier unit trouble hdbg62 HVAC 18 06-29-2011 09:57 PM
new r-410a ac unit installation procedure(w/old unit r-22)? excalibur1 HVAC 0 06-06-2011 04:47 PM
Window A/C Unit and Supplying Power JayEnder Electrical 1 04-30-2011 08:50 PM