AC Cycles On/off (too?) Frequently - HVAC - DIY Chatroom Home Improvement Forum
Old 08-31-2012, 01:37 PM   #1
Rewards Points: 127
AC cycles on/off (too?) frequently
Hi all,
I had a new HVAC system installed. These days we regularly experience 100-degree temperatures. The AC seems to kick on every few minutes.
Is there (should there be) a hysteresis adjustment in my programmable thermostat?
Should I set it for a two (or 3 or 4) degree window?
Thanks for your suggestions,
Daneel
Daneel is offline   Reply With Quote
Old 08-31-2012, 02:57 PM   #2
Rewards Points: 610
doesn't sound like it's the TT. I suspect some other limit control but I am not an AC Tech so, not sure what it might be. Maybe a low temperature lockout to prevent coil freezing or something like that OR shutting down due to system coolant pressure control? Might be best to get a certified techie in there.
techpappy is offline   Reply With Quote
Old 08-31-2012, 05:35 PM   #3
Which thermostat do you have?
Old 08-31-2012, 06:31 PM   #4
hello . the a/c unit shouldnt cycle on/off that fequently it shud pull it down in temp then cycle off need more info ,,,
hvac dude is offline   Reply With Quote
Old 08-31-2012, 07:24 PM   #5
kanhaihem you will knoe y it happen
put ur gauges on it will show you the problem
kanhai is offline   Reply With Quote
Old 09-01-2012, 01:33 PM   #6
Rewards Points: 127
found the manual!
Hello again,
Finally found the manual, inside of another HVAC manual. It is a Lennox ComfortSense Model L7742U 7-day programmable thermostat.
Page 24 begins a discussion of "Stage Delay and DIfferential Settings". It looks like Stage 1 (not sure there is a Stage 2) has a default differential of -0.5 to +0.5 deg, but could be set for a larger range.
This is in a category called "Installer Settings". I figure if I am careful not to change anything, I can at least scroll through various settings, take notes and learn more about what I have and how it is set up. Any warnings to the contrary???
Thank you,
Daneel
Old 09-01-2012, 01:42 PM   #7
Rewards Points: 610
takes longer than 3 mins to change room temp even only 1/2 degree so, I don't think widening the diff will change the situation..doesn't cost anything to try though...I don't think you can screw up the settings too much..if you do ..just remove TT and battery ..then re install ..should go to default factory settings..there may even be an APP for that on the TT..Good Luck!
Old 09-01-2012, 01:56 PM   #8
HOTDAWG
Have you tried calling the installers back again.. before you go changing setting I would call them and explain whats going on... for warranty reasons
Affordable Comfort, assisting with furnaces Barrie and surrounding area, as well as offering 24 hour furnace repair
Acomfort is offline   Reply With Quote
The Following 2 Users Say Thank You to Acomfort For This Useful Post:
COLDIRON (09-04-2012), hvactech126 (09-01-2012)
Old 09-01-2012, 03:55 PM   #9
biggles's Avatar
is the stat over the tru unit return and no getting direct discharge air on it? might want to widen that range too close..short cycling the condenser
Old 09-01-2012, 06:49 PM   #10
That's the correct setting to change if you want a wider swing.
Old 09-01-2012, 09:40 PM   #11
Rewards Points: 127
a table of on/off times...
At 17:12 I turned on the AC and set it to cool to 79 deg.
Local Cycle Cycle
Time Start Temp Duration
17:12 ON 85 30 min
17:42 OFF 80 3 min
17:45 ON 80 9 min
17:54 OFF 80 4 min
17:58 ON 80 6 min
18:04 OFF 80 4 min
18:08 ON 80 6 min
18:14 OFF 80 6 min
18:20 ON 80 4 min
18:24 OFF 80 8 min
18:32 ON 80 4 min
18:36 OFF 80 6 min
18:42 ON 80
I am going to keep logging for a while, then record Thermostat settings and fiddle a little.
This just seems like too many cycles for the condenser. I don't really know this. I am guessing that cycling it on-and-off is more wear and tear than leaving it on longer with fewer cycles -- like a light bulb. Is this right?
I have a call into the field engineer who last serviced the HVAC system.
Thanks,
Daneel
Old 09-01-2012, 09:46 PM   #12
Rewards Points: 127
thermostat vs. return air path
The thermostat is in a short, wide downstairs hallway, off a direct return path from the second floor to the return air register.
The Following User Says Thank You to Daneel For This Useful Post:
Missouri Bound (09-01-2012)
Old 09-01-2012, 10:36 PM   #13
An old Tradesmen
Rewards Points: 6,124
Set for a larger swing. Sounds like your A/C is a bit over sized.
Old 09-01-2012, 11:13 PM   #14
Rewards Points: 610
review TT manual..there should be a differential setting for ON OFF i.e. looks like existing diff is only 1/2 degree...Increase it to 2 degrees...should stop at 80 and NOT come back on until 82..or variation thereof.. if yoy manage to reset differential and find 82 too warm then just set stat at 77 it should then cycle between 79 and 77 and should run longer between cycles..note that it ran 30 mins to go from 85 to 80 therefore 2 degree diff should run about half that time..12 - 15 mins...I would think that is an improvement but still a little short...maybe the fan speed should be lowered a little
Old 09-02-2012, 10:12 AM   #15
Keep scrolling through the options until you come to compressor protect. Turning that on will give you 5 minutes minimum between cycles.
Williamson gas furnace cycles frequently after running for several minutes parpat HVAC 3 10-25-2011 05:37 PM
Furnace cycles on/off firozhirji HVAC 7 03-28-2010 06:08 AM
Furnace cycles too frequently wildfire46 HVAC 2 12-27-2009 05:42 PM
AC cycles frequently when on ZJChaser HVAC 4 10-26-2009 10:33 PM
oil furnace cycles frequently rachs79 HVAC 4 04-18-2007 07:36 PM