AC Condenser Frozen Low Superheat - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-15-2012, 07:00 AM   #16
UPdate: I removed the register covers, hooked up my gauges and ran for 20 minutes here are my results
low side pressure 67 psi 39 degrees
suction line temp 42 degrees
outside air temp 90 degrees
super heat = 3 degrees
My sub cooling
230 psi 111 degrees
liquid line temp 103 degrees
although my pressure is higher, my superheat got lower, so I shut it down and cleaned the coil with coil fin cleaner and rinsed with water, when i restarted ac after ten minutes my reading were all different and lines were frosted.
low side pressure 51 psi 27 degrees
suction line temp 29 degrees
super heat = 2 degrees
My sub cooling
208 psi 102 degrees
liquid line temp 98 degrees
JKV no harm done. understandable
timbo61 is offline   Reply With Quote
Old 06-15-2012, 12:26 PM   #17
Can't check with frost. SH and SC low could be a restriction
Could also be under charged with a blower motor going out. Need to verify air flow is correct.
Old 06-15-2012, 02:50 PM   #18
An old Tradesmen
Rewards Points: 6,124
When you cleaned the oil. Did you clean it from the discharge side, or its air inlet side?
Condenser fan airflow direction?? nicksab HVAC 8 09-20-2011 10:24 PM
Carrier Condenser Unit Screwed? gimmes name HVAC 6 07-24-2011 08:05 AM
Goodman Fan Condenser Replacement Help bigjohnstud4200 HVAC 2 07-03-2010 02:54 PM