#1 |
AC Condenser (compressor and fan) can't start
My 5 Ton AC condenser worked well last year but it is not working this year.
Both compressor and condenser fan are not running. The situation is below: 1. There is a AC power 110V between 2 hot lines on the contactor input terminals before turning on the AC. But this power is gone after turning on AC (24 V on). So both motors can't start. 2. When turning off the AC (24 V off), the 110 V is back. What's wrong with this problem? Somewhere short? Relay bad? Are all wires connected correct (see attached picture and diagram)? Brand: Bryant Product: 561CJX060000AAAA Model: 561CJ060-A Serial: 2300E23243 (see attached model plate) Please advise, thanks. Rick |
#2 |
you require 230 vac at the line side of the contactor...
| The Following User Says Thank You to carmon For This Useful Post: | plummen (05-01-2012) |
#3 |
I know the compressor is running at 230V. But each line in is 115V from the power circuit. How can get 230 between 2 input lines?
#4 |
I'm Your Huckleberry
You need to check across one leg to the other, from one terminal to the other at the contactor, and see if you have 240-ish volts. If not, you've got an electrical problem such as a bad breaker.
Thanks. |
| The Following User Says Thank You to Doc Holliday For This Useful Post: | plummen (05-01-2012) |
#5 |
230V with meter on both in coming line wires to the top of the contactor...and 24Vs on the 2 blue wire nuts.witht he condenser disconnect off that contactor should pull in from a call for cooling from the stat....don't check the incoming 230 to ground check between legs each 115V to ground
| The Following User Says Thank You to biggles For This Useful Post: | plummen (05-01-2012) |
#6 |
Also, do you have an electrical disconnect at the unit, with fuse perhaps? Check across the poles there as well.
Thanks. |
#7 |
So you mean between 2 black lines to the input of contactor should be 220vac, but I measured it is 110vac only. I'll check it on the circuit beaker. But I wonder why this 110vac gone when turning 24v switch on? Will this problem go away when the 220vac is normal? Thanks.
#8 | |
AC Condenser (compressor and fan) can't startQuote:
You're missing one leg of 120v.
Thanks. |
#9 |
I found one input line burned in the circuit beaker box but don't know why.
Question: Is my compressor still good as the follow measurement? CR = 0.4 ohm (blk-yel) CS = 1.9 ohm (blk-blu) SR = 2.2 ohm (blu-yel) I have known SR=CR+CS, from this formula, compressor should be fine but I wonder why the resistance is so small between 3 terminals. Please advise: Is the compressor good (not short)? It is 5 ton compressor. Last edited by rliu; 05-01-2012 at 10:53 PM. |
| Tags |
condenser fan motor, hvac compressor, start relay & capacitor ![]() |
| Display Modes | |